Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


While giving Power Supply of 24 VDC to a Transmitter,why
Shield Terminal is connected either at Transmitter or at
ISB.Why not Shield Terminal connected at both ends.If the
Reason is to avoid Noise interference,which type of noice
that is interfering.Is the Noice from the 24 VDC supply
terminals or from any external source.



While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Tr..

Answer / carl_ellis

1) A shield (screen) connected at both ends will carry
ground loop current due to the difference in ground
potentials at each end. A shield (screen) carrying current
will induce noise into the wires it is shielding.
Historically, shields (screens) have been connected at one
end only, typically at the receiver
(DCS/PLC/PAC/RTU/controller) end.

Current thinking as outlined in IEC 61000-5-2
Electromagnetic compatibility (EMC) - Part 5 Installation
and mitigation guidelines - Section 2: Earthing and cabling,
recommends grounding the shield at each
end for point-to-point and at every point for multi-drop.
Two point grounding provides protection against EMC and for
safety as well. However, this method assumes that all
points are on the same ground (i.e. use an equipotential
grounding grid).

Typically, Siemens has adopted this recommendation for
Profibus DP, an RS-485 multi-drop network. Of course, the
gotcha is "all points at the same ground potential". Not
in the real world, Mr. Siemens.

2) Although 24Vdc power supplies can be noisy, major
manufacturers produce DC power supplies with very little
ripple and excellent regulation.

DC power supplies used for HART need to meet the HART spec:
Maximum ripple (47 to 125 Hz) = 0.2V p-p
Maximum noise (500 Hz to 10 kHz) = 1.2 mV rms
Maximum series impedance (500 Hz to 10 kHz) = 10 ohm

24Vdc power supplies are not typically the source of noise

Carl Ellis
Measure First

Is This Answer Correct ?    5 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

What are the Components of Siemens S7 300 Series PLC system ?

1 Answers   Siemens,


What is voltage regulator?

0 Answers  


how we are selecting instuments by differentiating certain instruments in 4 to 20 ma range and certain in 1 to 5 v dc

0 Answers  


what is the si unit of pressure?

6 Answers   HTA Instrumentation,


difference b\w a transducer and a sensor

4 Answers  


when a magnet is heated?

0 Answers  


Is wet leg type system nessesary to measure water level of steam DRUM? How the transmitter is calibrated to measure this level?

0 Answers  


We have yokogawa cs3000 one fcs and 4 his. After download to his, showing successfully at es, but not transferred to his.

1 Answers   Shyam Steel,


Why Ma signal is using for control system?

1 Answers   Petrofac,


in split range control valve,two valve should be in two different line and that should have some distance,and we have only one positioner feed back link.so how we connect one feed back in two control valves?if you have picture please forward me.my email id kb.syamkumar@gmail.com

2 Answers  


what is axial shift n what is differential expansion in turbine? how many sensor probes r mounted for this n how it works?

2 Answers   Apple,


one rtd sensor which is connected at middle of distillation column where actual temp. is 100deg but when we tight this sensor at thermowell end it goes down to 90 deg & when remove from the thermowell(but sensor end dipped in well) showing actual reading, what is reason?

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)