Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


While giving Power Supply of 24 VDC to a Transmitter,why
Shield Terminal is connected either at Transmitter or at
ISB.Why not Shield Terminal connected at both ends.If the
Reason is to avoid Noise interference,which type of noice
that is interfering.Is the Noice from the 24 VDC supply
terminals or from any external source.



While giving Power Supply of 24 VDC to a Transmitter,why Shield Terminal is connected either at Tr..

Answer / carl_ellis

1) A shield (screen) connected at both ends will carry
ground loop current due to the difference in ground
potentials at each end. A shield (screen) carrying current
will induce noise into the wires it is shielding.
Historically, shields (screens) have been connected at one
end only, typically at the receiver
(DCS/PLC/PAC/RTU/controller) end.

Current thinking as outlined in IEC 61000-5-2
Electromagnetic compatibility (EMC) - Part 5 Installation
and mitigation guidelines - Section 2: Earthing and cabling,
recommends grounding the shield at each
end for point-to-point and at every point for multi-drop.
Two point grounding provides protection against EMC and for
safety as well. However, this method assumes that all
points are on the same ground (i.e. use an equipotential
grounding grid).

Typically, Siemens has adopted this recommendation for
Profibus DP, an RS-485 multi-drop network. Of course, the
gotcha is "all points at the same ground potential". Not
in the real world, Mr. Siemens.

2) Although 24Vdc power supplies can be noisy, major
manufacturers produce DC power supplies with very little
ripple and excellent regulation.

DC power supplies used for HART need to meet the HART spec:
Maximum ripple (47 to 125 Hz) = 0.2V p-p
Maximum noise (500 Hz to 10 kHz) = 1.2 mV rms
Maximum series impedance (500 Hz to 10 kHz) = 10 ohm

24Vdc power supplies are not typically the source of noise

Carl Ellis
Measure First

Is This Answer Correct ?    5 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

why level transmitter input is given 4to20ma

2 Answers   Sabic,


Capacitance, resistance ( colour coding ), parallel & series circuits.

0 Answers   CCIE,


what is sequence table in DCS . make a logic in sequence table for tripping of ID fan in Boiler(in YOKOGAWA CS 3000 DCS).

1 Answers   Yokogawa,


Wht should be the ratio of natural frequency (Fn) to wake frequency (Fw) and wht if goes above the rato limit?

2 Answers  


please can anyone tell me in detail, what's mean by open loop and close loop?

6 Answers  


diffrence b/w accuracy and precision?

4 Answers   HPCL,


in the pipe line if the control valve fails to respond to controller action,by what means we can stop the flow in the pipe line ?

9 Answers  


a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?

1 Answers  


how can we calibrate RADAR LEVEL transmitter 0% to 100%

3 Answers   Chevron Phillips, Honeywell,


What is Erosion in a control valve?

0 Answers   CCIE, Fisher,


i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....

0 Answers  


What will the new flow factor if D/P Transmitter is RE-RANGED from 25" WC to 50" WC

3 Answers   ADMA OPCO,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)