While giving Power Supply of 24 VDC to a Transmitter,why
Shield Terminal is connected either at Transmitter or at
ISB.Why not Shield Terminal connected at both ends.If the
Reason is to avoid Noise interference,which type of noice
that is interfering.Is the Noice from the 24 VDC supply
terminals or from any external source.
Answer / carl_ellis
1) A shield (screen) connected at both ends will carry
ground loop current due to the difference in ground
potentials at each end. A shield (screen) carrying current
will induce noise into the wires it is shielding.
Historically, shields (screens) have been connected at one
end only, typically at the receiver
(DCS/PLC/PAC/RTU/controller) end.
Current thinking as outlined in IEC 61000-5-2
Electromagnetic compatibility (EMC) - Part 5 Installation
and mitigation guidelines - Section 2: Earthing and cabling,
recommends grounding the shield at each
end for point-to-point and at every point for multi-drop.
Two point grounding provides protection against EMC and for
safety as well. However, this method assumes that all
points are on the same ground (i.e. use an equipotential
grounding grid).
Typically, Siemens has adopted this recommendation for
Profibus DP, an RS-485 multi-drop network. Of course, the
gotcha is "all points at the same ground potential". Not
in the real world, Mr. Siemens.
2) Although 24Vdc power supplies can be noisy, major
manufacturers produce DC power supplies with very little
ripple and excellent regulation.
DC power supplies used for HART need to meet the HART spec:
Maximum ripple (47 to 125 Hz) = 0.2V p-p
Maximum noise (500 Hz to 10 kHz) = 1.2 mV rms
Maximum series impedance (500 Hz to 10 kHz) = 10 ohm
24Vdc power supplies are not typically the source of noise
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
䑰ҕ䔈ҕ䖠ҕ䘰ҕ䛀ҕ䝐ҕ䟐ҕ䢐ҕ䥐ҕŹ
Technician A says the brake warning light is connected into both the parking and service brake systems. Technician B says the brake warning light will come ON only if the service brake system fails. Who is correct?
how to trim the pressure transmitter ?
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
-200mmwc to 500mmwc range transmitter have there 4mA is -200 and 20mA is 500.what is the range in 12mA?
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
Is there’s power on the bus (if so, state whether on the signal bus, or on a separate in the following: a) HART b) Profibus DP c) Profibus PA d) DeviceNet e) Foundation Fieldbus
what is the daily job of an instrument commissioning supervisor
purpose of absolute ppressure transmitter applcation?
you must show the examples application and give at least 4 types of transducer/sensors that can minimize the failure during the manufacturing of the resistors.
What is the use of double seated valve?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)