While giving Power Supply of 24 VDC to a Transmitter,why
Shield Terminal is connected either at Transmitter or at
ISB.Why not Shield Terminal connected at both ends.If the
Reason is to avoid Noise interference,which type of noice
that is interfering.Is the Noice from the 24 VDC supply
terminals or from any external source.
Answer / carl_ellis
1) A shield (screen) connected at both ends will carry
ground loop current due to the difference in ground
potentials at each end. A shield (screen) carrying current
will induce noise into the wires it is shielding.
Historically, shields (screens) have been connected at one
end only, typically at the receiver
(DCS/PLC/PAC/RTU/controller) end.
Current thinking as outlined in IEC 61000-5-2
Electromagnetic compatibility (EMC) - Part 5 Installation
and mitigation guidelines - Section 2: Earthing and cabling,
recommends grounding the shield at each
end for point-to-point and at every point for multi-drop.
Two point grounding provides protection against EMC and for
safety as well. However, this method assumes that all
points are on the same ground (i.e. use an equipotential
grounding grid).
Typically, Siemens has adopted this recommendation for
Profibus DP, an RS-485 multi-drop network. Of course, the
gotcha is "all points at the same ground potential". Not
in the real world, Mr. Siemens.
2) Although 24Vdc power supplies can be noisy, major
manufacturers produce DC power supplies with very little
ripple and excellent regulation.
DC power supplies used for HART need to meet the HART spec:
Maximum ripple (47 to 125 Hz) = 0.2V p-p
Maximum noise (500 Hz to 10 kHz) = 1.2 mV rms
Maximum series impedance (500 Hz to 10 kHz) = 10 ohm
24Vdc power supplies are not typically the source of noise
Carl Ellis
Measure First
| Is This Answer Correct ? | 5 Yes | 0 No |
in sports(eg,cricket) what is the technique for measurement of speed of the ball thrown by the bowler.
what is the way of measuring air flow in air duct?explaim instruments used and DP creation in line?
what is gas metering system? gas chromatograph? and gas compressors?
loop chech tools list
Whether the DI, DOs shields can be connected with Analog Input Shield Earthpit?
define optical temperature detector
please can anyone tell me in detail, what's mean by open loop and close loop?
i want to know the interview format fot gail, instrumentation. pls answer me in habib.sami1003@gmail.com
Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.
What is the difference between relative vibration
Can we measure pressure using differential pressure transmitter? If yes then how?
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)