What is correction factor in Tan delta test?
on site the ambient / atmp temperature is different.
whereas the facotry test conducted may be at different
temp .
As such to compare the value we apply a correction factor
such that the values are converted to a std test
temperature and we can have a comparsion of the obtained
results.
| Is This Answer Correct ? | 4 Yes | 3 No |
Is there possible to Test Transformer for Overfluxing Capability. Or is there any firm who does Overfluxing Test on Transformer?
how the transformer stables out zone faults? Because we use non directional O/C relays .Is there any special considerations are taking into account to overtake this?
Why is transformer core is earthed
What are the testing to be done before the installation of 1000 KVA Transformer?
What is the Difference Between resistance and resistivity?
wat s reactive power.... how could it be compensated.....
we convert 66kv to 33 kv to 11kv to 440v. why can't we directly convert 33kv to 440 ?
What is the difference between isolators and electrical circuit breakers? What is bus-bar?
How to select earthing strip for 100kw induction motor ?
why contactor not provided between output of VFD and motor?
if the voltage across the lamp drops by 1%, the power drawn will be reduced by how many %?
AVR is used for the Voltage regulation of the Generator using the feedback signal by exciting the field winding of the generator.But how the field winding will be excited & using what?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)