Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


for 644KW load which MCCB should i use

Answers were Sorted based on User's Feedback



for 644KW load which MCCB should i use..

Answer / wareagle

You have not given the required information to answer your
question. Voltage? power Factor? Type Load? Fault current?

Is This Answer Correct ?    6 Yes 2 No

for 644KW load which MCCB should i use..

Answer / karthik ccel

If i consider your 644kW load as a motor then,

I Assumed some parameters are:
644kW Motor, Power Factor - 0.9, Efficiency - 0.9, Load
Connected Voltage - 415V Then,


I = (644*1000) / (1.732*415*0.9*0.9) = 1106Amps
Considering 20% Margin = 1106 * 1.20 = 1327Amps

Conclusion:
So, We can choose Breaker rating is higher than that
1327Amps. Generally no one use the MCCB breaker above
800Amps. So, we can prefer the 1600Amps VCB Breaker for that
644kW Load.

Is This Answer Correct ?    6 Yes 3 No

for 644KW load which MCCB should i use..

Answer / antaratara ghosh

assuming the load as motor,operating voltage as 415 V,pf
as .85, efficiency as .95,

rated current, Ir= (644)/(1.732*0.415*0.85*0.95)
= 1110 A (approx)
now considering VFD starting for the motor,
starting current, Ist= 2*Ir
= 2220 A
considering margin of 20%, maximum current flowing =
2220*1.2 = 2664 A

Since MCCB are not used above 630 A in India, you have to
go for 3150 A (which is just greater than 2664 A and
available in market) ACB...

Is This Answer Correct ?    2 Yes 2 No

for 644KW load which MCCB should i use..

Answer / lokeshraj

Use 1600 Amp ACB.

Is This Answer Correct ?    0 Yes 1 No

for 644KW load which MCCB should i use..

Answer / ahmed raza

Formulla for calculation of breaker is...
Total load in Watts/380(voltage)*0.8(pf)*1.732(delta to Y
conversion)
So
= 644/380*0.8*1.732
= 1223.10
we can say
= 1250AMPs breaker should be use....

Is This Answer Correct ?    0 Yes 3 No

for 644KW load which MCCB should i use..

Answer / sami

Calculate 644kw load Amp
Breaker Selection Formula ( Amp*125% )
for Example : 1000A*125%=1250
Instal 1250Amp Breaker

Is This Answer Correct ?    1 Yes 5 No

Post New Answer

More Electrical Engineering Interview Questions

What will be the current if the resistance total in a series circuit doubles?

0 Answers  


why generaotr rating is in kva and dc motor in kw?

7 Answers   Bhel, NTPC,


what is meant by negative conductor?

2 Answers  


tell me any book for current n potential trasformer with full knowledge ?

1 Answers  


what are the reasons of low voltage during start the DG?

1 Answers   Godrej, Tata Power,


We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.

0 Answers  


how to choose the cable size for 100A(is there any formula please update)

6 Answers  


why are transformers rated in KVA and not in KW

8 Answers   ABB, Bosch,


why high current produce in case of transformer when turns are internally gets shorted.

3 Answers   TCS,


write a c++ code that receives an integer number and display the sum of the number and its revers integer?

0 Answers   MIT,


why starting current is high and resistance is almost 0 during the starting of motor dc motor...?

0 Answers  


What is maximum load capacity of 800 VA inverter?

5 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)