for 644KW load which MCCB should i use
Answers were Sorted based on User's Feedback
If i consider your 644kW load as a motor then,
I Assumed some parameters are:
644kW Motor, Power Factor - 0.9, Efficiency - 0.9, Load
Connected Voltage - 415V Then,
I = (644*1000) / (1.732*415*0.9*0.9) = 1106Amps
Considering 20% Margin = 1106 * 1.20 = 1327Amps
Conclusion:
So, We can choose Breaker rating is higher than that
1327Amps. Generally no one use the MCCB breaker above
800Amps. So, we can prefer the 1600Amps VCB Breaker for that
644kW Load.
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / antaratara ghosh
assuming the load as motor,operating voltage as 415 V,pf
as .85, efficiency as .95,
rated current, Ir= (644)/(1.732*0.415*0.85*0.95)
= 1110 A (approx)
now considering VFD starting for the motor,
starting current, Ist= 2*Ir
= 2220 A
considering margin of 20%, maximum current flowing =
2220*1.2 = 2664 A
Since MCCB are not used above 630 A in India, you have to
go for 3150 A (which is just greater than 2664 A and
available in market) ACB...
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ahmed raza
Formulla for calculation of breaker is...
Total load in Watts/380(voltage)*0.8(pf)*1.732(delta to Y
conversion)
So
= 644/380*0.8*1.732
= 1223.10
we can say
= 1250AMPs breaker should be use....
| Is This Answer Correct ? | 0 Yes | 3 No |
What will be the current if the resistance total in a series circuit doubles?
why generaotr rating is in kva and dc motor in kw?
what is meant by negative conductor?
tell me any book for current n potential trasformer with full knowledge ?
what are the reasons of low voltage during start the DG?
We have 5 Distribution sections with variable loads&We have 3 Gensets(500kva,380kva&250kva) our total load is between 400kva to 600kva. so how could we connect 3gensets.
how to choose the cable size for 100A(is there any formula please update)
why are transformers rated in KVA and not in KW
why high current produce in case of transformer when turns are internally gets shorted.
write a c++ code that receives an integer number and display the sum of the number and its revers integer?
why starting current is high and resistance is almost 0 during the starting of motor dc motor...?
What is maximum load capacity of 800 VA inverter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)