why are transformers rated in KVA and not in KW
Answers were Sorted based on User's Feedback
Answer / samir rana
cu lossof x mer depends on current and iron
loss on voltage total x mer loss depends on va and not on
phase angle between v and i it it is independent of load
power factor. that is why rating og x mers is in kva and
noy in kw.
| Is This Answer Correct ? | 20 Yes | 2 No |
Answer / mustakul
iron loss depends on voltage and copper loss depends on
current.so transformer rating is in KVA not in Kw
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / praneetha
cu loss of a transformer depends on current and iron loss
on voltage.hence total transformerloss depends on volt
ampere and not on phaseangle between them.it is independent
of p.f.that is why transformers is in KVAand not in KW.
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / nachu
Only the voltage (V) or Current (A) is stepped up or down and there is no change in the power (W). Power in this case is reactive power not active power so it is mentioned as KVA.
| Is This Answer Correct ? | 13 Yes | 13 No |
Answer / ahamadkutty
A transformer is rated in VA or kVA because the kVA is the
vector sum of Active power IR and Reactive power
IX(l-c)which a transformer can be delivered. So depending on
the connected load with active and reactive component the
power kW will be varied keeping the kVA maximm at the rated
kVA of the transformer.For a fixed voltage the current
supplied by the transformer is the maximum fixed by the
formula VA/V and maximum power by the load.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rahul rajpal
Transformer is not a load....That why it's rated in KVA
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / osman mehmetukaj
because to remain constant power transformer
while only changing currents and tension in the primary and
the secondary opposite, for example: Ip X Up =Is x Us =S
S(=)kVA
| Is This Answer Correct ? | 3 Yes | 7 No |
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.
I PURCHASED A DEISEL GENARATOR SET OF AVR TYPE& RATING 125KVA BUT SOME TIMES THE OUTPUT VOLTAGE IS FLUCTUATING WHAT ARE THE PROBABLE REASONS GIVE ME
how we can do the insulation on secondary of ct explain and so that tan delta will within limit
What is the maximum allowed kwa through 2.5mm cable. Electric company installed 2 electric meter at my premises . Two jumper wires of 2.5 mm are used to connect . 2 single phase meters with allowable load 6 and 3 kwa. These jumper wires are taken from a 3 phase electric meter. Meters are in open Sun. What max load these wires can take.
What is ignitor and why it is use in Hpmv lamp ?
hwat type of motor is used in thermal gas turbine hydro nuclear power plants and why
if 2 coil of 1000W connect in series and 200 v is applied across it . then what is the total power of coil when coil have only resistive load .
sometime battery charged and then automatically charged when rectifier ON conition, is there any chances please clarify the same.
What is different type of Electrical curve and how it protects the equipment's while up-normal situation?
What is the difference between isolators and electrical circuit breakers? What is bus-bar?
In Siemens S7-300 PLC, what is funtion and funtion block ? What is the difference between them ? When to use function and when to use function block
How can I indicate rpm on digital rpm meter with help of simple tacho output? tacho output is 90v at 3000rpm.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)