Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


I have 90KW Motor 60 Hz,380V Pf 0,88.
after testing the Motor without Load is the no load Current
36 A,but wenn i put load after 2 hours the current increase
more than 156 A.
Can anybode tell me waht is the Problem?

Answers were Sorted based on User's Feedback



I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current ..

Answer / linu mohan

motor full load current is 155-162A for different categories
of make;so check from which load the motor is connected
ex-compressor,pump or crusher likewise anything
1)compressor- air might have blocked in the filter due to
impurities in the air after few hrs,so motor taking high
current.
2)pump-jamming might have blocked in the filter due to
impurities in the water after few hrs,so motor taking high
current.
if the motor is kept in a closed atmospheric room then due
to heatness after few hrs motor will take full load current
&tripping occurs,so to avoid that; place an exhaust in there.

last option clear that its not a star delta feeder...


if then also problem is not solved&strikes again then it
comes under mechanical head for sure

Is This Answer Correct ?    2 Yes 0 No

I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current ..

Answer / michael

the simpliest answer to your question is in this example.

example you have to lift a 10 kg of rice, you use a little strength in order to lift it, but if your tying to lift a 50 kg of rice, you will exert much effort and strength in order to lift it. it is similar to the motor. if there is higher load the current will increase in order to satisfy the load required..

Is This Answer Correct ?    1 Yes 0 No

I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current ..

Answer / manish parekh

Dear Sir,
The 90KW motor FLC is approx 155Amp so the motor amp
increseing after load so load will be 100% on motor.

Is This Answer Correct ?    1 Yes 1 No

I have 90KW Motor 60 Hz,380V Pf 0,88. after testing the Motor without Load is the no load Current ..

Answer / ketan patekar

90 KW motor full load current carrying capacity is 236 ampere..
And yes when you connect load than afcourse your motor will carry ampere as per your load.
So here everything is ok.
If your motor carrying above 236 ampere current than there is some fault like your load is high or impeller or frame or design problem etc

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

how to calculate the voltage drop in electrical cable while laying cables?

2 Answers  


EARTH AND NEUTRAL ARE JOINTED OR NOT?

7 Answers  


why insulation cost is more in underground cable than in overhead line?

2 Answers  


I want to do a mini project. Now I'm studying in 6th semis tor EEE Engineering.

0 Answers  


lightning arrester rating selection procedure: (line to line voltage(kV)/(squ.root of 3))*squ.root of 2. now the question is, IS this above formula correct for both STAR and DELTA connected system???

1 Answers  


What are chief characteristics of state-space method and its techniques ?

0 Answers   Limton,


what is LUX?

4 Answers   NTPC,


in case of three phase induction motor,when it is connected to three phase supply,why the magnetic field is rotets around the armeture?

5 Answers   Hindalco,


Please explain, how to test vector group of tranformer(Delta y1) . Thank

0 Answers   PGCB,


what do you mean electrical earth pit?

2 Answers   Enercon,


We are having a 2000KVA DG set. It trips with Over speed and Engne Hot when the mahine is stopped in full speed. How shall I analyse the block load and reverse power.Is the problem related to power factor. The machine which runs on this DG is having all Synchronous motors with incividual Drives.

1 Answers  


what is the difference b/w UHVDC and HVDC(LIGHT)?

4 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)