Answer / shashikant
connect the LT capacitor to the 3 phase AC suply, measure
the current & line voltage in each phase. Get the reading.
Calculate kVAR using formula kVAR = 1.732*(Avg.Line Voltage)
*(Avg current)/1000
| Is This Answer Correct ? | 34 Yes | 6 No |
Answer / rajib
KVAR=KW(tan@1-tan@2)
Where, @1= system power factor, @2= desire power factor
For example. 500KW motor has system power factor 0.8 and we want to improve it 0.95
tan@1=tan cos-1(.8)=0.75
tan@2=tan cos-1(.95)=0.3287
KVAR=500(0.75-0.3287)=210.65=210KVAR
and so on
| Is This Answer Correct ? | 20 Yes | 0 No |
Answer / dharmvir prasad
present pf cos @1 = 0.76
desired pf cos @2 = 0.90
@1=cos- 0.76= 40.536
@2=cos- 0.9= 25.842
tan @1=0.855
tan @2=0.484
tan@1-tan@2=0.37
0.37x kw of motor
| Is This Answer Correct ? | 17 Yes | 1 No |
capacitance of the capacitor is mentioned in KVAR.
Formula : KVAR = KW*tan@
FOR tan@, First note the power factor & KW without
connecting capacitor.
The noted power factor is in cos@.Convert the cos@ value in
tan@.
for ex. If power factor is 0.6, KW = 200
cos@ = 0.6
cos-1 (0.6) = 53.1
tan (53.1) = 1.333
200*1.333 = 266.6 KVAR
if you use 266 KVAR capacitor, Then the power factor
improves to unity (1.000).
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / giribalaaji
can anyone plz derive the formula for required KVAR ?
Required KVAR= KW* (tan@1-tan@2) i want to know how tan comes in the equation.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mukesh tyagi
Above Answer is correct , so i agree with this perfectlty.
| Is This Answer Correct ? | 7 Yes | 6 No |
I would like to say that p.f =KW/KVA AND FORMULA IS KVAR =ROOT OF (KVA)SQURE -(KW)SQURE . THIS IS RIGHT ONE FORMULA
| Is This Answer Correct ? | 1 Yes | 0 No |
What is the distance between the EHV lines and also the distance for earth ??
what is the difference b/w ground & virtual ground?
why we use to transmit the power in three phases intead of single phase ?
how will i find Transformer rating if supply voltage is 11k.v and how will i find incomer if transformer rating is 12MVA
I want definition for ABT Meter (Availability Based tariff) ?
0 Answers Radha Regent Hotels,
effect of decrease in excitation?
Tell me all plants load factors i.e which plant operating on which load?
how do you measure earth leakages in 3phase wires?
what solid earthing means?
Can We Apply DC POWER To Transformer???? And Why????
Before i went to bed my master bathroom lights were working fine. At 2 am, when I went to use the lights, none of them were working. The outlets throughout the bathroom work, but the lights and fan above the toilet don't. I have two panels of switches. The one panel has four switches. One of the switches turns on the hall light, and that works. The other three are to other lights, and they don't. The other panel has three switches. One of those is to the fan, and the other is to a light above the toilet. The other is a to light that is also on that other panel. I tried the breakers, and the one that turns off the outlets, marked for the bathrooom, turns on and off the outlets. None seemed to be tripped. I checked the lightbulbs, and they are fine. Please help
What is the unit of vaccum?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)