How to calculated capacitor rating both HT
Answers were Sorted based on User's Feedback
Answer / shashikant
connect the LT capacitor to the 3 phase AC suply, measure
the current & line voltage in each phase. Get the reading.
Calculate kVAR using formula kVAR = 1.732*(Avg.Line Voltage)
*(Avg current)/1000
| Is This Answer Correct ? | 34 Yes | 6 No |
Answer / rajib
KVAR=KW(tan@1-tan@2)
Where, @1= system power factor, @2= desire power factor
For example. 500KW motor has system power factor 0.8 and we want to improve it 0.95
tan@1=tan cos-1(.8)=0.75
tan@2=tan cos-1(.95)=0.3287
KVAR=500(0.75-0.3287)=210.65=210KVAR
and so on
| Is This Answer Correct ? | 20 Yes | 0 No |
Answer / dharmvir prasad
present pf cos @1 = 0.76
desired pf cos @2 = 0.90
@1=cos- 0.76= 40.536
@2=cos- 0.9= 25.842
tan @1=0.855
tan @2=0.484
tan@1-tan@2=0.37
0.37x kw of motor
| Is This Answer Correct ? | 17 Yes | 1 No |
capacitance of the capacitor is mentioned in KVAR.
Formula : KVAR = KW*tan@
FOR tan@, First note the power factor & KW without
connecting capacitor.
The noted power factor is in cos@.Convert the cos@ value in
tan@.
for ex. If power factor is 0.6, KW = 200
cos@ = 0.6
cos-1 (0.6) = 53.1
tan (53.1) = 1.333
200*1.333 = 266.6 KVAR
if you use 266 KVAR capacitor, Then the power factor
improves to unity (1.000).
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / giribalaaji
can anyone plz derive the formula for required KVAR ?
Required KVAR= KW* (tan@1-tan@2) i want to know how tan comes in the equation.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mukesh tyagi
Above Answer is correct , so i agree with this perfectlty.
| Is This Answer Correct ? | 7 Yes | 6 No |
I would like to say that p.f =KW/KVA AND FORMULA IS KVAR =ROOT OF (KVA)SQURE -(KW)SQURE . THIS IS RIGHT ONE FORMULA
| Is This Answer Correct ? | 1 Yes | 0 No |
how solar power plant energy meter multiplication factor
My question is abt backlog.I had dropped one subject in my second year, and completed this subject in the 3rd attempt, so how many backlogs i have got?1 or 3?plz sujjest the answer as soon as possible
what is the magnitude of earthing and neutral voltage
there are cam operated switches - why we call cam operated , What is cam ?
What are the protections to be used for Generator?
if an insulated power and control cables of a running gas diesel gensets laid direct in an open trench i.e, trench bed is not rcc of a power house in which rain water, spillage water alwas exists and all power control cables remains submerged even when gas gensets of 480 kw each runningin on load. These power &control cables runs from power house to switchgear room through these trenches in which water remains most of the time. pl explain its merit & de-merit
What safety followup during kWh meter isolation
why buchholz relay is kept on inclined position and why it is cover??
What are the tests carried out on transformer while testing at sites?..Pls explain me in detail
what do you mean by class PS CT and what are technical details needed for calculating it?
Moving Iron instruments are applicable with a) DC only b) AC only c) DC & AC
14 Answers Bhel, Engineers India, Engineers India Limited,
What is function for Load Bank test and why need to test.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)