Answer / shashikant
connect the LT capacitor to the 3 phase AC suply, measure
the current & line voltage in each phase. Get the reading.
Calculate kVAR using formula kVAR = 1.732*(Avg.Line Voltage)
*(Avg current)/1000
| Is This Answer Correct ? | 34 Yes | 6 No |
Answer / rajib
KVAR=KW(tan@1-tan@2)
Where, @1= system power factor, @2= desire power factor
For example. 500KW motor has system power factor 0.8 and we want to improve it 0.95
tan@1=tan cos-1(.8)=0.75
tan@2=tan cos-1(.95)=0.3287
KVAR=500(0.75-0.3287)=210.65=210KVAR
and so on
| Is This Answer Correct ? | 20 Yes | 0 No |
Answer / dharmvir prasad
present pf cos @1 = 0.76
desired pf cos @2 = 0.90
@1=cos- 0.76= 40.536
@2=cos- 0.9= 25.842
tan @1=0.855
tan @2=0.484
tan@1-tan@2=0.37
0.37x kw of motor
| Is This Answer Correct ? | 17 Yes | 1 No |
capacitance of the capacitor is mentioned in KVAR.
Formula : KVAR = KW*tan@
FOR tan@, First note the power factor & KW without
connecting capacitor.
The noted power factor is in cos@.Convert the cos@ value in
tan@.
for ex. If power factor is 0.6, KW = 200
cos@ = 0.6
cos-1 (0.6) = 53.1
tan (53.1) = 1.333
200*1.333 = 266.6 KVAR
if you use 266 KVAR capacitor, Then the power factor
improves to unity (1.000).
| Is This Answer Correct ? | 20 Yes | 12 No |
Answer / giribalaaji
can anyone plz derive the formula for required KVAR ?
Required KVAR= KW* (tan@1-tan@2) i want to know how tan comes in the equation.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mukesh tyagi
Above Answer is correct , so i agree with this perfectlty.
| Is This Answer Correct ? | 7 Yes | 6 No |
I would like to say that p.f =KW/KVA AND FORMULA IS KVAR =ROOT OF (KVA)SQURE -(KW)SQURE . THIS IS RIGHT ONE FORMULA
| Is This Answer Correct ? | 1 Yes | 0 No |
Are Refrigerators & Deep Freezers the Inductive load ? How to calculate the Power Factor & hence the Output Power for them ?
how to select a circuit breaker?
24 Answers ABB, BARC, TCS,
when running 2 nos 450kva dg sets in parallel operation ,in one Dg set power factor and Kvar going to lagging and ampere suddenly going high,please give me suggestion to correct the same.
Does magnetomonopoles exists? one maxwell equation strongly suggests no, but how about their existance in plasma?
How many types oil using in transformer ? How many letars using in transformer..?
difference between diode and scr?
if we have 320KVA Genset kindly advice how much load we can put it.
Why frame of the motor is specified?. If we mention KW and voltage level,automatically frame is decided or separately frame is compulsory to mention?.
Can double compression glands be used with regular cables?
what is the suitable voltage of transmission line to transmit 10000w power through 250 km. (a)11kv (b)33kv (c)66kv (d)132kv ]and please tell me whats the logic behind it
Explain (in simple ) - root mean square. whats its role in electrical fundamandal.where its used
In n high voltage 11kv system What happened if 1 of CT cable (IDMT) loose.Will e/f or o/c trip.please explain detail
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)