The reason you are getting tripping of the RCBO is the way
the RCBO works.
The RCBO senses the current in the phase and neutral. As
long as these are balanced it will not trip. It is designed
to trip if there is an inbalance. This is usually a current
flow between the phase and earth which is then not returned
by way of the neutral.
When the is a short between the earth and the neutral it
provides a parallel circuit. Some of the current will flow
through the earth and some through the neutral as they are
now connected together on both sides of the RCBO. The RCBO
senses an inbalance because not all of the phase current is
flowing back thriough the neutral and it therefore trips.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.prakashchandra
If there is a loose connection in the neutral wire ,neutral
point gets shifted to the point of loose connection at the
incoming.Then there will be some voltage in the neutral wire
beyond it, resulting in flow of current when in contact with
the earth wire.
| Is This Answer Correct ? | 0 Yes | 1 No |
why the desirable efficiency for a motor is 60%, but in case of transformer, it is above 90%?
WAHAT IS ELECTRICITY
How to measure the Harmonic Distortion of UPS ie THD?
What is phase angle? and what is importance to measure it?
What is a dc motor?
Can u start a tube light without a starter?
State the formula for overall efficiency of thermal power station
why DG rating in kva
What is the function of neutral CT in transformer? Turn ratio of typical CT for 2MVA transformer ? or relation between full load current of transformer and neutral CT ?
1 Answers Electrical Inspectorate,
what is the difference between delta-delta, delta-star transformer???
why is the rating of transformer done in kva and not in kw.
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)