we convert 66kv to 33kv then 33kv to 11kv,11kv to 440v.why
not we convert directly from 66kv to440v?
Answers were Sorted based on User's Feedback
Answer / shariff
It can be step down from 66kV to 440V,but the problem is
above 33kV power transformers will be in treated as EHV,
and normally they will carry loads in terms 20 or 12.5MVA
etc. then for e.g for 20MVA the sec. current with 440V will
be 20x10E6/440=45kA( Normal rating), where this power
transformer cant be made practically with huge cuurent. So
practically we will go for 66kV to 11kV normally, where
Current is the limiting factor...
| Is This Answer Correct ? | 32 Yes | 4 No |
Answer / k.prakashchandra
Inside a factory it is feasible.But for public utility you
can not erect regular 66KV/433V substations say ,every 500
meters, as long LT distribution lines can not drawn in view
of current and voltage drop.
| Is This Answer Correct ? | 11 Yes | 3 No |
It increases the power transmission cost very high.
| Is This Answer Correct ? | 8 Yes | 2 No |
Answer / jaheerabbas
if we are converting the 33Kv to 440v directly, wastage of
power is more in the form of heat,so that we required large
no of heat sink too....heat sink cost will be more compare
to transformer, so that we go for the step by step convertion
| Is This Answer Correct ? | 14 Yes | 10 No |
Answer / lakesh thakur
when we convert 66kv to 440v directly then transformer size
will increase & loses will also increase. So we should
increase the size of heat sinke. So directly we can say the
cost of whole our project will increase & also increase MVA
rating
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / ved prakash
Basic insulation level at HV & LV side is also a big factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ramki
fulls , there is mutual coupling in between the windings , so for 66/33/11/133..like this we can found the mutual coupling as a nearly 1.......so wethis
| Is This Answer Correct ? | 2 Yes | 11 No |
If we have a 2000kva load,How much kvar capacitors we go to add to improve the power factor at 0.9?pls give the calculation and fully theory?
How can we calculate the rating of capacitor bank to be connected for a particular load(ex.100kw)to improve the power factor from 0.8 to 0.9?
what is differant beetween overload current and phase current?
why do we use 3 single phase instead of one 3 phase?? though vee connection is its advantage but what is the hidden reason behind it??
(1)WHAT HAPPENS WHEN SUDDENLY LOAD GIVEN TO THE INDUCTION MOTOR ? (2)CAN WE MAKE WOOD AS MAGNET ? (3)WHAT IS THE VALUE OF MAGNETIC FLUX DENSITY IN TRANSFORMER ? (4)WHY WE ARE USING ELECTROMAGNETI NOT ELECTROSTATIC IN MACHINE ?
is a normal conductor can be used a core in windings if not what is the winding core speciality.
Any one can explaination about calibration with rotating sub standards?
FRIENDS, I am doing DEEE (part time)final year. Give me some ideas for project
MICOM P122 OC/EF RELAY HAVE HARMONIC RESTRAIN OR NOT?
I FINISHED MY B.TECH IN EEE . I AM IN NEED OF A GOOD TRAINING INSTITUTE TO DO COURSES .. CAN ANYONE SUGGEST GOOD CENTRES IN TAMILNADU ,BANGALORE ,OTHER AREAS???????
why the transformer neutral give to the earth ?
whats the advantage and disadvantage in TUMETIC mdel transformer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)