In transformer which temp should be less oil temp are
winding temp?
Answers were Sorted based on User's Feedback
Answer / sathiyamurugna
normally oil temperature should be less compared to winding
temperature because transformer oil used for cooling the
winding. if oil temperature should not go high other wise it
will not cool the winding properly
Is This Answer Correct ? | 39 Yes | 0 No |
Answer / vishal ingle
in normal condition, oil temperature should be less
compared to winding temperature because transformer oil is
used for cooling the winding. oil takes away the heat from
winding resulting in reduction of temperature. Also for
natural heat flow the oil temperature should be less than
winding temperature.
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / siddesh cs
under normal condition,transformer oil as low temperature compared to lv & hv winding because, oil is mainly used for cooling purpose as per the law of thermodynamics heat flows from hot end to coold end so heat transfer from winding to oil.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / karthik
should be oil temp is less, oil is used for cooling the transformer
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prabhakar jha
oil temperature should be less then winding temperature.winding temperature depends on Load.so oil temperature should be less for cooling transformer winding..
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / pritesh
Obviously Oli temperature should be less than winding temperature because oil immersed tc oil basically use for heat dissipation and cooling so oil temp less
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anupama
the external or u can say the temprature of ur surrounding
should be less than both because ultimately heat is
disspated in surroundingsss
Is This Answer Correct ? | 0 Yes | 2 No |
How can be decreased the size of transformer?
What is difference between mcb and mccb.
why 3 phase motors are preferable over single phase motors ?
on a three-winding transformer relationship delta-delta-star, on third winding why the relationship is a star? what are the advantages and disadvantages? Thank you and please help
What are the conditions for sustained oscillator or what is backhouse criterion?
How to megger test 11 kV cable and the acceptance IR value
advantage and disadvantage of team work?
eddy current losses depends on?(a-max magnetic feild,b-avg magnetic feild,c-on frequency,d-on square of frequency)?
HOW TO CALICULATE THE LEAD ACID BATTERY AH AND HOW TO FIND THE 1.2KVA UPS BACKUP @ 1000WATTS LOAD?
An AC coil to give DC supply whats happen in the coil.what type of problem are create.
how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???
from generating station If 400v LT line length is 1000m how much voltage is drop and how do i calculate it? which cable will be use for this line?