In transformer which temp should be less oil temp are
winding temp?
Answer Posted / sathiyamurugna
normally oil temperature should be less compared to winding
temperature because transformer oil used for cooling the
winding. if oil temperature should not go high other wise it
will not cool the winding properly
| Is This Answer Correct ? | 39 Yes | 0 No |
Post New Answer View All Answers
what are the types of electromagnetic forces developed in practical transformer?
what is the voltage rating of chiller unit sensors
Write the analogous electrical elements in force current analogy for the elements of mechanical translational system.
how to find out cable size if load is 2800 watts, 230 volts AC supply and load distance is 1800 meters
Why let through energy not considered for ACB breaker while cable sizing?
hello friends..... any one have papers or any study materials?sail ,hpcl...?
What are the causes for the failures of sandwich type (Al) busducts?
is it possible to have dc motors on single chip
The efficiency of a 100kva transformer is 0.98 at full load as well as half load , for this transformer what is the Copper loss at full load ?
What is the classification of hydro projects based on installed capacity?
explain the function of brush less dc motor?
Why we use ups battery and dsdb battery in thermal power plant
harmonics filter
how many current required for hypo test
When we connect the large capacitor bank in series ?