what is the different between earth leakage relay and earth
fault relay?
Answers were Sorted based on User's Feedback
Answer / swapnil
earth leakage relay : monitirs the leakage current
continously and ir connected in earthign wirr
Earth fault relay oprates on earth fault. It detects earth
fault whenever there is short in between phase and earth
| Is This Answer Correct ? | 25 Yes | 5 No |
Answer / ugrasen
earth leakage relay monitoring the leakage current in mA
Earth fault relay operat on earth fault. It detects earth
fault whenever there is short in between phase and earth.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / muhammad umair
Both Take their sensing from a ring core CT. In earth
leakage relay sensing is high i.e in mA.Where as earth fault
relay is used on higher loads where sensing is low i.e in A.
This is why earth leakage is used for the house hold devices
or power supply sockets protection. And Earth fault relay is
use for Industrial loads,motors normally more than 37KW (Not
a standard),distribution,generation etc.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / meghraj kabdule
earth leakage relay used in DC battery charger to monitor
DC leakage. And earth fault relay is used for lines &
transformer backup protection.
| Is This Answer Correct ? | 8 Yes | 24 No |
What is means by MacAdam Ellipse?
Can anyone provide with a SLD for HT panel installation for a 33KV line and distribution end has three 1.5MV transformers. Is it suitable to use OCB or VCB and also provide me the suitable rating and its connection diagram.
Explain Power factor in simple words
What are the three types of compensators?
Is any generator is developed which is operated with out diesal or other expensive source?
what is AB switch???
What are unstable systems?
in VFD when freq is reduce the voltage will reduceor not if it will reduced upto ...
why are the a.c.series motors preferred for electric traction
what is the vvvf in the dumbwaiter?? or lift. what is the actual process?/
What is the minimum load that you can keep in a 3 Phase 40 KVA Diesel Generator? Is it neccessary to load all the 3 phases? Can a phase be left without load?
how does induction motors works.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)