In 16' pipeline one pcv is installed which is controlled by
PT installed at inlet of PCV.If Flowrate in pipeline
increases what will happen to pressure at the inlet of pcv.
Answers were Sorted based on User's Feedback
Answer / kuber
The pressure will be proportional to the flow rate, as the
flow rate increases the pressure at inlet of the valve will
increase. then the valve starts to close relatively.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / r.murugan
if pressure transmitter installed before pcv (example sp
10bar) suddenly pipe line flow increase pressure will
increase but as long as controller an auto controller will
give command to open the valve to maintain the setpoint pressure
if flow rate is less pressure is coming down less than
setpoint controller will give command to close the valve to
maintain the pressure (if pressure tapping before control
valve)
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / triptisliet@gmail.com
according to bernauli's theorem total enerngy will remain
same so if velocity increases then pressure decreases.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / tony lorenzo
If the controller is in Auto that time, and provided its been tuned, the pressure should remain as is. The PCV valve should open as expected, how much? we dont know.
| Is This Answer Correct ? | 2 Yes | 2 No |
why we use impulse line of flow transmitter at 45 deg. angle both side of orifice plate.
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
HOW DPT WORKS?
What Is Pre- Commissioning Package +what is DCS & ESD Pre- Commissioning for Instruments Please explain your answer on practical ground base
Difference between ultra sonic flow meter
I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
how to calculate temp.prapotional to mv in thermocoulpe.
how to calibrate 0- 150 psi presure gauge by dead weght tester
If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?
where do you give the 4-20 ma i/p in a MIL control valve?
wt kind of business we can do by usig PLC?
Why humidity limit is 30 to 55 % for raw material storage?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)