If a differential pressure transmitter is calibrated for
0~2500 mmH2o and transmits a 4~20mA dc signal. The
transmitter is placed across an orifice plate which is sized
to create 2500 mmH2o differential at 5000m3/Hr
a) what is the flow rate when the transmitter signal is
13.0mA DC?
b) what is the signal output of the transmitter when flow
rate is 2500 m3/Hr ?
Answers were Sorted based on User's Feedback
Answer / nani babu
a) flow rate for 13mA is 2812.5 m3/hr
b) 12 mA to 2500 m3/hr
Is This Answer Correct ? | 24 Yes | 6 No |
Answer / nabil amrani
a) Y=(20-4)/(5000-0)*x + b=16/5000*x + 4
when y = 13 mA x = (13-4)* 5000/12 = 2812.5 m3/Hr
b) Y=16/5000 * x + 4
when x= 2500 y= 16/5000 * 2500 +4 = 12 mA
Is This Answer Correct ? | 8 Yes | 3 No |
Answer / raju
ans a)=√(13-4/16)×5000=3750 m3/hr
b)=(2500/5000)×(2500/5000)×16+4= 8 mA
Is This Answer Correct ? | 13 Yes | 13 No |
How the sizing of the analog signal cable is calculate?
On liquid service if PT Head is 18 meters. How much pressure will be exerted on it. If Transmitter is not in service?
how to overhaul control valves.what are the proper procedures.
what is the protection system in solar turbine compressor
What is the working principle of sox, nox analyzer?(opacity monitor) Otherwise how to measure the sox,nox?
How to work temperature gauge?
What do you need to consider when installing a flowmeter
how u meassure a room temp?in rtd or themo couple?
define SIMULATION a and what is the need of it
Explain Difference between Bech set and operating range of control valve
How does electro magnetic pump works ?
hi,i am doing 3 year in electronic and instrumentation engineering. what type of aptitude questions will be asked in a core industries and how can i improve my skills in instrumentation?