If a differential pressure transmitter is calibrated for
0~2500 mmH2o and transmits a 4~20mA dc signal. The
transmitter is placed across an orifice plate which is sized
to create 2500 mmH2o differential at 5000m3/Hr
a) what is the flow rate when the transmitter signal is
13.0mA DC?
b) what is the signal output of the transmitter when flow
rate is 2500 m3/Hr ?

Answers were Sorted based on User's Feedback



If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc si..

Answer / nani babu

a) flow rate for 13mA is 2812.5 m3/hr
b) 12 mA to 2500 m3/hr

Is This Answer Correct ?    24 Yes 6 No

If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc si..

Answer / nabil amrani

a) Y=(20-4)/(5000-0)*x + b=16/5000*x + 4
when y = 13 mA x = (13-4)* 5000/12 = 2812.5 m3/Hr

b) Y=16/5000 * x + 4
when x= 2500 y= 16/5000 * 2500 +4 = 12 mA

Is This Answer Correct ?    8 Yes 3 No

If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc si..

Answer / rajaravindra

A)1581.25m3/h
B)15.31mA

Is This Answer Correct ?    1 Yes 0 No

If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc si..

Answer / raju

ans a)=√(13-4/16)×5000=3750 m3/hr
b)=(2500/5000)×(2500/5000)×16+4= 8 mA

Is This Answer Correct ?    13 Yes 13 No

If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc si..

Answer / mani

a)Ans 4062 m3/hr

b)Ans 8 mA

Is This Answer Correct ?    6 Yes 11 No

Post New Answer

More Instrumentation Interview Questions

How the sizing of the analog signal cable is calculate?

0 Answers   Reliance,


On liquid service if PT Head is 18 meters. How much pressure will be exerted on it. If Transmitter is not in service?

1 Answers  


how to overhaul control valves.what are the proper procedures.

1 Answers   Jindal, QAFCO,


what is the protection system in solar turbine compressor

0 Answers  


What is the working principle of sox, nox analyzer?(opacity monitor) Otherwise how to measure the sox,nox?

1 Answers   Thermax,






How to work temperature gauge?

0 Answers   KJS,


What do you need to consider when installing a flowmeter

2 Answers  


how u meassure a room temp?in rtd or themo couple?

4 Answers  


define SIMULATION a and what is the need of it

3 Answers   Siemens,


Explain Difference between Bech set and operating range of control valve

3 Answers  


How does electro magnetic pump works ?

1 Answers   IGCAR,


hi,i am doing 3 year in electronic and instrumentation engineering. what type of aptitude questions will be asked in a core industries and how can i improve my skills in instrumentation?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)