I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
Answers were Sorted based on User's Feedback
Your tx's range is 0~10000mmwc if u
use it at 0~1000mmwc head press tank
than it will indicate 10% level when tank
full. So just calibrate it (configure it) at
0~1000mmwc before take inservice for
actual reading of tank at output
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / ys
u can use this transmitter. but u should rerange the
transmitter.(ie if tank service is water and ur lt is dry
leg type,then LRV=0 and URV=1000MMH2O.. If ur lt is wet leg
calibrated, then LRV= -1000 AND URV=0 MMH2O)
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
I have a LT of 10000mmwc range. can i use this LT in
1000mmwc range of tank?? if yes than what happened???
A change from a range of 10000 mmwc to 1000 mmwc is a turn
down of 10:1
If your transmitter supports a minimum range of 1000 mmwc
within the accuracy spec you require, then re-range the
transmitter and use it.
Most smart DP transmitters from major manufacturers will
support this.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
what are the diff. in servo and regulatory control?
How to calibrate a orifice differential pressure flow transmitter in process?
loop chech tools list
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
Explain about safety integrated level protection? . How it was differ from other protections ?
Give 2 application of quartz crystal used for process parameter measurement.
for commissioning the DPT and Flow Transmitter , what kind of necessary activities we have to check and do? specially that orifice flange valve[ isolation valve}
State some of balance principle’ advantages?
How a oxygen sensor & analyzer work at boiler or furnace, what’s the principle & science is beyond this, How O2 sensor scene & convert signal & move toward analyzer & analyzer show reading in percent?
1 Answers GS Engineering Construction, KNIC,
can any one explain in which term we are flow flow is it volumetric r is it mass? and y
What is rtd output signal
what will the sending unit in the fuel gauge utilizes?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)