I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
Answers were Sorted based on User's Feedback
Your tx's range is 0~10000mmwc if u
use it at 0~1000mmwc head press tank
than it will indicate 10% level when tank
full. So just calibrate it (configure it) at
0~1000mmwc before take inservice for
actual reading of tank at output
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / ys
u can use this transmitter. but u should rerange the
transmitter.(ie if tank service is water and ur lt is dry
leg type,then LRV=0 and URV=1000MMH2O.. If ur lt is wet leg
calibrated, then LRV= -1000 AND URV=0 MMH2O)
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / carl_ellis
I have a LT of 10000mmwc range. can i use this LT in
1000mmwc range of tank?? if yes than what happened???
A change from a range of 10000 mmwc to 1000 mmwc is a turn
down of 10:1
If your transmitter supports a minimum range of 1000 mmwc
within the accuracy spec you require, then re-range the
transmitter and use it.
Most smart DP transmitters from major manufacturers will
support this.
Carl Ellis
Measure First
| Is This Answer Correct ? | 1 Yes | 0 No |
tell me the temp range of rtd?
Hi Friends , i need one urgent help , i am preparing for M.tech entrance examination , i need some obejective questions related to instrumentation field. where can i get those ? can anyone help me pls ?
what is the difference between auto tuning and manual tuning of controllers(eg:PID,PI,PD CONTROLLERS )
What is the function of SMPS
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
Identification of control valve parts.
0 Answers CCIE, Oil and Gas Jobs,
What is modbus?
If fire would be inside the plant which fire detector is to detected the fire.
which instrument is used to study the structure of phloem and xylem tissue?
In thermocouple could we use the lug for termination or not,Thermocouple is any time,I am currently concerned with K type.please let me know if anybody know
4 Answers Saudi Aramco Shell Refinery Company SASREF,
What is the procedure of calibration of Load cell?
what is the responsibility of an instrument commissioning supervisor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)