How to zero trim the level transmitter by using foundation fieldbus communicator.
Answers were Sorted based on User's Feedback
Answer / larry gremillion
To set the zero trim for K-TEK (a member of the ABB group) Foundation Fieldbus level devices:
1. In the Transducer Block enter the following – exactly as typed – into the CONFIG_ACCESS field:
KTEKFACTORY
Write the change to the device. This will change the GENERAL_STATUS field to ‘Access Factory’ before changes can be made and saved.
2. Move the float on the probe to the lowest position. This point is TRIM_POINT_LO.
3. Set the CONFIG_VALUE to the level value (in inches) of the lowest float position (typically 0”). In the CONFIG_METHOD field of the transducer block select TRIM_POINT_LO from the pull-down menu. Write the changes to the device. When the value in the TRIM_COUNT_LO field changes to match the value in the SENSOR_RAW_LEVEL_1 field the change has been saved.
4. Exit ‘Factory Access’ mode by typing a minus sign into the CONFIG_ACCESS field and write to the device, or by cycling power to the device. This completes the sensor trim procedure for K-TEK Foundation Fieldbus level transmitters.
7. Manually copy all settings and values from SENSOR_RANGE in the Transducer Block to the XD_SCALE in the AI Block (CH 1). When these data are written to the device they will automatically be copied into the relevant parameters in the Transducer Block.
I hope this helps!
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ram nath singh
first I will go to (Hart application-on line application-device setup-diag/ service-calibration-sencer trim) I can choos zero trim for T Tx.
Is This Answer Correct ? | 2 Yes | 2 No |
what is effect of specific gravity in differential level transmitter , explain formula related with this .
0 Answers Flour Tech Engineers (P) Ltd,
Explain the functions of the CPU of a PLC.
why we use 24 vdc in instruments mostly?
What is cold junction compensation in thermocouples? How is it achieved?
Q- Ordinary Water Tap is which kind of controller ? P , PI or PID i chose the option of ON - OFF type controller but ambiguity is that for different positioning of tap we get different flow
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
what is the difference about HART, and 4-20mA signal?
what is the significance of hook up
I have installed a RTD whose length is 2250mm(RTD stem length), but it's upper 200 -250mm is out of the reactor, and this upper 200mm stem is surrounded by atmospheric temp. And the lower portion i.e. 2000mm is in contact with the measuring fluid, then does the final measuring temp. Gonna change as the upper 200mm RTD stem is out of reactor?
1 Answers Process Control Technologies,
What are different types of control valves?
how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..
2 Answers Agi Glaspac, Reliance Power,
hi this is noor i wnt know the procedure and precations errection for PRESSURE AND DP transmitters? how to take impusle line for level and flow?(water and steam) impulse line sizes? and type of material ? plz give me answer / reffer any website ? to me "mail2noor.hyd@gmail.com"