How to zero trim the level transmitter by using foundation fieldbus communicator.
Answers were Sorted based on User's Feedback
Answer / larry gremillion
To set the zero trim for K-TEK (a member of the ABB group) Foundation Fieldbus level devices:
1. In the Transducer Block enter the following – exactly as typed – into the CONFIG_ACCESS field:
KTEKFACTORY
Write the change to the device. This will change the GENERAL_STATUS field to ‘Access Factory’ before changes can be made and saved.
2. Move the float on the probe to the lowest position. This point is TRIM_POINT_LO.
3. Set the CONFIG_VALUE to the level value (in inches) of the lowest float position (typically 0”). In the CONFIG_METHOD field of the transducer block select TRIM_POINT_LO from the pull-down menu. Write the changes to the device. When the value in the TRIM_COUNT_LO field changes to match the value in the SENSOR_RAW_LEVEL_1 field the change has been saved.
4. Exit ‘Factory Access’ mode by typing a minus sign into the CONFIG_ACCESS field and write to the device, or by cycling power to the device. This completes the sensor trim procedure for K-TEK Foundation Fieldbus level transmitters.
7. Manually copy all settings and values from SENSOR_RANGE in the Transducer Block to the XD_SCALE in the AI Block (CH 1). When these data are written to the device they will automatically be copied into the relevant parameters in the Transducer Block.
I hope this helps!
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ram nath singh
first I will go to (Hart application-on line application-device setup-diag/ service-calibration-sencer trim) I can choos zero trim for T Tx.
| Is This Answer Correct ? | 2 Yes | 2 No |
What is difference between flame retardant & flame resistance cable? Among which type of cable is used for ESD & Fire and Gas system application?
How to calculate mmwc values into tonnes?
How to Calibrate Transducers? Can you give me a step by ste procedure?
What's the Installtion procedure of DP Transmitter for Gas,steam and water?
diff between neutral ,ground,phase , earthing and shielding?
Capacitance, resistance ( colour coding ), parallel & series circuits.
What should be the main consideration while starting the Rotating compressor when we dont know the cut in and the cut off pressure setting of the pressure switch
Please asked me How calculate DCS controller memory.
Watt is Wrms define rms?
what do you know about Foundation Fieldbus?
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
why cant we use mV instead of mA?
12 Answers ABB, Power Grid, Qatar Gas, USW, Visa Steel,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)