Follow Our FB Page << CircleMedia.in >> for Daily Laughter. We Post Funny, Viral, Comedy Videos, Memes, Vines...


i have D.p. transmitter of range 0 to 2540 mmWC, i want to
use this for flow measurement (0 to 500 ltr/hr.) what
should i do?

Answers were Sorted based on User's Feedback



i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / g.ramakrishnan

to install flow transmitter and correct range
orifice,ensure that ft output is linear means dcs side u
have to make sq root.if smart type transmitter means
configured sq root output field itself.then u will get
correct reading.

Is This Answer Correct ?    16 Yes 3 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / bari

Install appropriate dp flow element in the flow line with
Beta ratio corresponding to dp of 2540 mmWC for flow of 500
ltr/hr.

Is This Answer Correct ?    14 Yes 5 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / raees mansoori

use this formula to dcs side Q=K*A*sqrt(H/P) or configured
sqrt output to transmitter side.

Is This Answer Correct ?    9 Yes 1 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / k.sreenivasan

Mr.PasavaRaj,
Your question misses a major point.
Do you have a flow sensor (like orifice or annubar etc)
already installed?If yes, Then you have to match the DP
required by the sensor to the transmitter DP Range.Please
note that 2540 mm wc of the transmitter range can be
changed using communicator (If it is HART) based on
transmitter specifcations.Check what is the minimum span
the tranmitter can be calibrated? if that is greater than
the sensor DP, you have to look for another transmitter.

Is This Answer Correct ?    5 Yes 0 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / pasuvaraj

mr Raees,

Can u explain wat u mean for H & P in this formula, and
also can u explain how the pressure units convert in to
flow rate in the transmitter. I Mean that mm of water colum
is converted into Mass or volumetric flow can u give me the
answer

Is This Answer Correct ?    3 Yes 1 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / jigarsinh vaghela

First of all Good Question

Ans: Use Orifice Bore Calculation sheet
you want process data like pipe size, Max Temp, Max Pressure,
Max Flow rate & Application like Steam or water
put this values in OPA Calculation sheet & you would got dp
range in MMWC

Is This Answer Correct ?    0 Yes 0 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / nadeem iqbal

Dear Sir,if i have flow transmitter range 0 to 2500 mmwc and my DCS range is 0 to t m3/hr ,i m getting 9 Ma how much will be the delta P

Is This Answer Correct ?    0 Yes 0 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / sanjay

by creating proper DP across orifice plates we can measure
flow rate also change the SQRT property in x-mitter

Is This Answer Correct ?    2 Yes 3 No

i have D.p. transmitter of range 0 to 2540 mmWC, i want to use this for flow measurement (0 to 500..

Answer / guruprasad s.v

i am guruprasad honewell employer.

defenetly we can change configure, this fecility is there
in our company.

Is This Answer Correct ?    5 Yes 8 No

Post New Answer



More Instrumentation Interview Questions

There are two chlorination tonners both are connected to two pressure swithes and the pressure switch is connected to SOV which operates the valve to changeover the tonner selection i.e if pressure one tonner goes low the other tonner should come in line if it is inautomatic selection design a circuit using relays ?

0 Answers  


What is Difference between PLC and CNC ?

2 Answers  


What is the cascade control

0 Answers  


What is rang ability?

0 Answers  


In turbine what does term CDP, NH, HSSOC means.

0 Answers   Takreer,






Boiler flame scanner working principle?

1 Answers   Bhel,


What is 1:1 redundancy ?

0 Answers  


what the differant between Wet Leg /Dry Leg

2 Answers   Sepam Group,


How would you choose differential range?

0 Answers  


what is the input of conductivity sensor and meter during the calibration time and what is the output?

2 Answers  


How to measure Flow of air line,what is the procedure of creating DP in line to measure Flow!

3 Answers  


How to get Cv of control valve having following parameter ,i.e inlet pressure 4.5kg/cm2 outlet pressure 1 kg/cm2 specific gravity 0.808

3 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (5075)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4444)
  • Electrical Engineering Interview Questions Electrical Engineering (16600)
  • Electronics Communications Interview Questions Electronics Communications (3915)
  • Chemical Engineering Interview Questions Chemical Engineering (1092)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (214)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (258)
  • Instrumentation Interview Questions Instrumentation (2987)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (123)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (0)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1377)