i have D.p. transmitter of range 0 to 2540 mmWC, i want to
use this for flow measurement (0 to 500 ltr/hr.) what
should i do?
Answers were Sorted based on User's Feedback
Answer / g.ramakrishnan
to install flow transmitter and correct range
orifice,ensure that ft output is linear means dcs side u
have to make sq root.if smart type transmitter means
configured sq root output field itself.then u will get
correct reading.
| Is This Answer Correct ? | 17 Yes | 3 No |
Answer / bari
Install appropriate dp flow element in the flow line with
Beta ratio corresponding to dp of 2540 mmWC for flow of 500
ltr/hr.
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / raees mansoori
use this formula to dcs side Q=K*A*sqrt(H/P) or configured
sqrt output to transmitter side.
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / k.sreenivasan
Mr.PasavaRaj,
Your question misses a major point.
Do you have a flow sensor (like orifice or annubar etc)
already installed?If yes, Then you have to match the DP
required by the sensor to the transmitter DP Range.Please
note that 2540 mm wc of the transmitter range can be
changed using communicator (If it is HART) based on
transmitter specifcations.Check what is the minimum span
the tranmitter can be calibrated? if that is greater than
the sensor DP, you have to look for another transmitter.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / pasuvaraj
mr Raees,
Can u explain wat u mean for H & P in this formula, and
also can u explain how the pressure units convert in to
flow rate in the transmitter. I Mean that mm of water colum
is converted into Mass or volumetric flow can u give me the
answer
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / jigarsinh vaghela
First of all Good Question
Ans: Use Orifice Bore Calculation sheet
you want process data like pipe size, Max Temp, Max Pressure,
Max Flow rate & Application like Steam or water
put this values in OPA Calculation sheet & you would got dp
range in MMWC
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nadeem iqbal
Dear Sir,if i have flow transmitter range 0 to 2500 mmwc and my DCS range is 0 to t m3/hr ,i m getting 9 Ma how much will be the delta P
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sanjay
by creating proper DP across orifice plates we can measure
flow rate also change the SQRT property in x-mitter
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / guruprasad s.v
i am guruprasad honewell employer.
defenetly we can change configure, this fecility is there
in our company.
| Is This Answer Correct ? | 5 Yes | 8 No |
can we create an interrupt in plc through scada?
If i have 4 Allen Bradely make RS logix 5000 PLC and for viewing that we are using 4 RS view SCADA for 4 different packages. Now, I will want to view two packages on only one SCADA. Then how i will do it?
explane hart protocol? what is its advantages.
how to measure low temperature(<100 dec celsisus) with non condact sensor
what is linerity and non-linearity?
why metallic housing is provided of solenoid valve.
give eg of how I/P is used in control loops
WHY WE WILL USE 0-24VdC IN ELECTRONIC CIRCUITS AND INSTRUMENTATION TRANSMITTERS?
3 Answers Aban Power, Jindal, JSW, Sugar Factory,
how the presure switches are calibrated? and what happen inside?
Make a ladder diagram on LSL valve will close, on PSL valve will open and start the motor
what is the difference between RTU & MTU in SCADA system?
Profibus DP is a multi-master system. Would it work on RS-485 4W or not, and justify your answer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)