Why do we use 24V DC supply in instrumentation? What are its
merits and demerits??
Answer / amith
As per ISA standards 24 VDC is the minimum possible voltage
at which the spark will not come,we know our transmitters
will give max output current of 27 mA here they have limit
This current because the power we get is less than 1 watt
(P=VxI)648mW which is not capable of producing a spark thus
they have avoided spark generation by selecting 24 VDC and
limiting currnt to 27mA.this comes under extrisic safety.
| Is This Answer Correct ? | 33 Yes | 5 No |
Describe the concept of Gain Scheduling, as currently found as an option in some controllers.
how can we measure the level measurement with the help of pressure gauge?
How can we measure the level of a closed system like drum
What is the difference between fire detector and smoke detector?
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
what is metal of piston ring
why 4-20 mA signal is preferred over a 0-10V signal
Regarding MOS (maintenance override switch), I want to know its function and its state ( 1 or 0 when not activated ). An example will be very helpful..thank you.
in differential pressure transmitter,min&max pressure range for hp&lp
How to connect field devices to PLC and DCS using a FIELD BUS, DP,MOD BUS(please tell me any extra interfce or adopters need in this case if we use remote i/o s)
What is the differaence between PLC and DCS?
what r the different types of instrumentation cables? give their specification?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)