d/p flow transmitter LP side give to pressure.what you
geting out put ? how you get(ma)?
Answers were Sorted based on User's Feedback
Answer / nilesh karpe
Dp- transmitter workes on Differential pressure.the
pressure difference between low and high pr. side.for eg,
pressure on high side is 2Kg/cm2 & on low side is 1.5Kg/cm2
then D.P. will 0.5 KG/CM2.
in conterol terms the diaphragm element senses this 0.5
KG/cm2 & generate output curresponds to signal.The input of
transmitter is 24 V DC signal .& is converted to 4-20 MA
output according to the callibration range.
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / naga manikandan
If u r giving presssure to only LP side not HP side the mA
output will be -ve(i.e it will go below 4mA) and the
reading will be in -ve side.
| Is This Answer Correct ? | 16 Yes | 4 No |
Answer / jazz
Dp transmitters work by measuring the difference between the
pressure measured on the high pressure port (HP) and the low
pressure port (LP). If for example the pressure on the HP is
100 psi and the pressure on the LP is 75 psi, the DP
transmitter will measure the difference of 25 psi. Let say
for example that the dp transmitter range is calibrated from
0 to 50 psi dp, the transmitter will output a proportional
12 mA (representing 50% of the dp range) The 24VDC supply on
serves to give power to the transmitter electronics so that
the transmitter will output a proportional 4-20mA signal
corresponding to the pressure difference sensed by the
pressure ports.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / carl_ellis
A loop powered transmitter's output can NEVER go to 3.0 mA
or 2.0 mA or 1.5 mA because this range is the electrical
current used to run the transmitter's electronics. A 2 wire
transmitter needs about 3.6 mA just to run its own
electronics. A 2 wire transmitter can only go as low as 0.1
or maybe 0.15mA below the nominal 4.0mA 'zero' to 3.9 mA or
3.85 mA.
But, 4.0 mA can be a negative number. There can be pressure
ranges of
-0.5 bar to - 0.8 bar
-0.5 bar to 0.0 bar or
-0.5 bar to +1.0 bar or
If the high side is left open to the atmosphere and a
pressure applied to the low side, the pressure will be
negative because a DP transmitter subtracts the low side
from the high side.
high side minus low side = pressure
atmosphere minus pressure = negative pressure
0 barg minus 0.5 barg = -0.5 barg
Just because the pressure is negative doesn't mean the
output has to be negative. The 4-20mA range just represents
a pressure range and that range can include a negative
pressures. The 4-20mA is interpreted as a positive or
negative value by the receiver, the
DCS/PLC/controller/indicator.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / imran yousaf
when we apply pressureon LP side only , then there will be some outpur in the form of mA, it does not matter it ll' be either +ve or -ve bcs current have no polarity value.
| Is This Answer Correct ? | 0 Yes | 0 No |
yahh for DP-transmitter we will be having the two taps at
the side or at the bottom side ,but to know the working of
the transmitter or for the calibration purpose we have
give/apply the pressure at LP-side tapping & the HP-side it
should be kept open for the atmosphere ,,,,,,,,,hence by the
difference of the pressure we will get the MA-output.,,i,e
with respect to the applied pressure
| Is This Answer Correct ? | 2 Yes | 10 No |
WHICH INSTRUMENT USED TO CALIBRATE CONTROL VALVE?
23 Answers Exxon Mobil, Honeywell,
What is ultrasonic flowmeter?
hello sir/madam, I,Subramanian need 5yrs placement papers of officer trainee of Instrumentation technology.pls send to this mail id mani_nxtgen@yahoo.co.in please do the needful. with regards, subramanian.v
What is difference between scada and virtual instrumentation?
what is working principle of presure and temperature guage?
How do Foundation Fieldbus works? how the Communication Carries out from Foundation field bus,Field Devices and Controller? Were it's Application in the Field? For Which Signals this is Used? PLease Find this answer for this Question Detaile wise because i want to clear the Concept Regarding Foundation Field Bus,if Possible please attach the link of Document with Contails Diagramatic So that more esier for me.
how can we tune a PID. If it is by zeiger nichols method..please explain briefly with help of an example.
How addressable fire systems work? Pl. send details with architect.(Loop), also send details regarding Gas system. Pl. help me.Thanks
how level can be measured in open tank with reference to pressure
why the derivative in PID is always set to zero?
What are the difference between mass flow meter, magnetic flow meter and vortex flow meter.
What happen if we install my pressure transmitter below the elevation of pipe in natural gas service?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)