is there any difference in reading or error in value, if we
connect the R phase in Y terminal and Y phase in R terminal
of electronic energy meter of 11 kv feerders???
Answer / k.prakashchandra
No. But corresponding CTs and PTs should not be
altered.Please note that the R, Y, B phases of one station
may be different from those of another station.In case of 11
KV, only phase sequence is considered. Energy recorded by
energy meter is the sum of individual measuring elements..