CAN WE CALIBRATE LEVEL TRANSMITTER USING HART
COMMUNICATOR WHEN WATER LEVEL IS PRESENT IN THE BOILER
SHELL?
Answers were Sorted based on User's Feedback
Answer / haparmar
Yes we can calibrate through Hart But care should be taken
that Drum level should be controlled
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / deepan
HART MEANS ITS NOT A CALIBRATOR.ITS A COMMUNICATION DEVICE USED ONLY IN SMART TX.
FIRST CONFORM IT GIVES ERROR READING.
IF LEVEL TX IN DRUM GIVE SOME EROTIC READING WE CAN JUST CHECK WHETHER THE TX RANGE & CONFIGURATION.SENSOR TRIM.
| Is This Answer Correct ? | 0 Yes | 2 No |
Answer / arinjoy dasgupta
Yes we can do online calibration using HART calibrator on
level t/x but we must see the level in the drum through the
gauge glass and also communcate the same with the operator
sitting in the DCS.
| Is This Answer Correct ? | 0 Yes | 3 No |
what is diff b/w neutron and ground?
i want the equation of this question. Tranmitter range is 120 mmwc and dcs flow range is 1700 nm3/hr. if i want to change dcs range from 1700 to 2400 nm3/hr then how much dp i have to enter in transmitter
what is the difference between plc & DCS?
5 Answers Cheminova, NGIL, Siemens,
How can we cheak the ENCODER ?
What is pre-commissioning and commissioning ?
what is the difference between plant earth and instrument earth? and what type of cable( cable size ) used for both? and why ?
When a timer is placed in RS Logix 5000 with preset value less than its scan time it is malfunctioning. i.e., if the preset is set to 30ms still the timer TT bit is counting till 150ms(its scan time). Any solution for the problem?
What is the differace between Volumatric flow meter and Mass flow meter.
what is difference b/w the solinoid volve and autodrain?
what are the documentation and instrument identification system used to identify the correct device to be calibrated? name atleast three.
a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?
What is derating factor in Motor?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)