Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


whycircuit breaker is not connected at the generator end
where the capacity of the generator is more say 60MW, 100MW
etc.

Answers were Sorted based on User's Feedback



whycircuit breaker is not connected at the generator end where the capacity of the generator is mo..

Answer / k.prakashchandra

Gen side means usually 11 KV.The generator current at full
load will be very high for 60 MW( 52.5 x MVA A)for an
indoor breaker .Therefore , synchronization and tripping on
fault are done at EHT breaker which is of above 110 KV.For
any fault between the breaker and gen ,the master trip is
employed ,which trips the field breaker ,CB and the governor.

Is This Answer Correct ?    13 Yes 5 No

whycircuit breaker is not connected at the generator end where the capacity of the generator is mo..

Answer / kunal singh dabi

Due to following points
1)Transient Recovery Voltage (TRV)
2)Higher X/R value
3) Delayed current Zero
circuit breakers was not used after above 60 MW generators.

However please note that now full line of IEEE C37.013
qualified medium-voltage vacuum generator circuit breakers
for voltages up to 24 kV and generators up to 200 MW for
both indoor and outdoor applications are available in
market.

Please note that Circuit breakers applied to generator
switching applications are subject to conditions quite
different than those of a normal distribution circuit
breaker used in industrial, commerical and utility systems.
Distribution circuit breakers, whether of the outdoor
substation type or of the drawout type for use in metal-
clad switchgear, conform to IEEE C37.04 (basis of ratings),
IEEE C37.06 (preferred ratings), IEEE C37.09 (testing) and
IEEE C37.10 (application.)

Is This Answer Correct ?    5 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between RMS meter and normal meter

3 Answers   TATA,


what is high and low cut off voltage of BB and DG at SPS????????

0 Answers  


What is the difference between circuit breaker and isolator

0 Answers  


what is VSWR?

1 Answers  


Tell me about yourself. ……………………………………. Why did you leave your last job? What do you see yourself doing five years from now? Ten years from now? What are your long-range career objectives? Why did you choose this career? How well do you work with people? Do you prefer working alone or in teams? How would a good friend describe you? What would your last boss say about your work performance? Why should I hire you? What makes you qualified for this position? What do you think it takes to be successful in a company like ours? In what ways do you think you can make a contribution to our company? What's the most recent book you've read? What two or three accomplishments have given you the most satisfaction? Why? Describe the most rewarding experience of your career thus far…………… Why did you decide to seek a position in this company? What can you tell us about our company? What do you know about our competitors? What two or three things are most important to you in your job? Are you willing to travel for the job?

0 Answers  


_____hamari_____tumhari____ne dil ki_____utari. _____ne ____ dekha ashe ___ doshti ko lage na hamari.Complete pajal

1 Answers   Microfine Industries,


why an ac solenoid valve attract the plunger eventhough we interchanges the terminal?will the ploes changes?

1 Answers  


i want to ask that as everybody knows that in star connection on star point is called neutral. my question is that why on that poin called neutral. what is the reason behind it. what is the logic behind it. i heared somewhere that on this point all phases current become zero thats why. if this answer is right then prove why on that point is current become zero. if this answer is not right then tell me the right answer. post ur answer here or on my mail address. m.ikram786@yahoo.com m.ikram555@gmail.com. thanks.

1 Answers  


WHAT IS THE FAULT WHEN 100HP TURBINE MOTOR TRIPS, LIST THE FAULTS AND ITS TRABULESHOOTING TIPS.. MY AUTO TARNSFORMER STARTER TRIPS

0 Answers   MPS Techologies,


roles of owslaw explain?

3 Answers   BSNL,


What do you mean by cold shinkable cable joint.How it is done.

0 Answers  


what is skin effect and corona discharge ?

4 Answers   Asian Paints,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)