whycircuit breaker is not connected at the generator end
where the capacity of the generator is more say 60MW, 100MW
etc.

Answers were Sorted based on User's Feedback



whycircuit breaker is not connected at the generator end where the capacity of the generator is mo..

Answer / k.prakashchandra

Gen side means usually 11 KV.The generator current at full
load will be very high for 60 MW( 52.5 x MVA A)for an
indoor breaker .Therefore , synchronization and tripping on
fault are done at EHT breaker which is of above 110 KV.For
any fault between the breaker and gen ,the master trip is
employed ,which trips the field breaker ,CB and the governor.

Is This Answer Correct ?    13 Yes 5 No

whycircuit breaker is not connected at the generator end where the capacity of the generator is mo..

Answer / kunal singh dabi

Due to following points
1)Transient Recovery Voltage (TRV)
2)Higher X/R value
3) Delayed current Zero
circuit breakers was not used after above 60 MW generators.

However please note that now full line of IEEE C37.013
qualified medium-voltage vacuum generator circuit breakers
for voltages up to 24 kV and generators up to 200 MW for
both indoor and outdoor applications are available in
market.

Please note that Circuit breakers applied to generator
switching applications are subject to conditions quite
different than those of a normal distribution circuit
breaker used in industrial, commerical and utility systems.
Distribution circuit breakers, whether of the outdoor
substation type or of the drawout type for use in metal-
clad switchgear, conform to IEEE C37.04 (basis of ratings),
IEEE C37.06 (preferred ratings), IEEE C37.09 (testing) and
IEEE C37.10 (application.)

Is This Answer Correct ?    5 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

which mm cable should be used for 1.hp immersible pump motor for the distance of 330 metres?

0 Answers  


1)Explain why the cradle guard is used on railway crossing in overhead line construction?

0 Answers  


1. What is differential relay? How it operates? 2.How to calculate the Short Circuit Impedance in Transformer? 3.What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works? 4. While testing the 33KV Busbar by using Hipot kit, what should be the test voltage we have to apply? 5. What is the procedure/activities to be taken to inject the current more than 2000A by using 2000A Loading Transformer? 6. Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example? 7. Why restricted earth fault protection is needed? Why can’t differential Protection is sufficient? 8. What should be the minimum and maximum ohmic value for earthing? 9. Why DC Currents are not used in transformer? 10. What is the Frequency while we step up the voltage from 220V to 11KV? Is it possible? Explain it?

0 Answers  


why lightning arrester and other equipment earthing conneting from same earth bar ?

1 Answers  


What is the implications when 600 hp motor is started when the unit is running with Transformer of capacity 1500 KVA and DG set of 1000kva

0 Answers   Shasun Chemicals,






how power trnafor from 1 point to another point in bus bar ya transmission line( voltage trnasfer from 1 point to another poin)

0 Answers   Suzlon,


Why the isolation treasforfer are connected at out put of the ups ig 200kva ??????????????????

3 Answers  


What are the usege & different between UPS & batteries with charging system in in Substation?( UPS 120V AC & battery charger is 120v DC)

1 Answers  


How to calculate the load loss and no load losses of the power Transformer? i am having the following details : full load ct : in AMP HV :1676 ; LV:31.5 1800 KVA ;33KV/620 V for wind mill applications

2 Answers   ReasonSoft,


What is time invariant system?

0 Answers  


What is STEP VOLTAGE ?

7 Answers  


I have running 4 generator in paralel.All generators Voltages is same(470 V),KW also same (100 KW) but only No2 generator Amper is high than another generators. DG No:1,3,4 470V,100KW, 150 A DG No:2 470V,100KW,400 A

4 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)