whycircuit breaker is not connected at the generator end
where the capacity of the generator is more say 60MW, 100MW
etc.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Gen side means usually 11 KV.The generator current at full
load will be very high for 60 MW( 52.5 x MVA A)for an
indoor breaker .Therefore , synchronization and tripping on
fault are done at EHT breaker which is of above 110 KV.For
any fault between the breaker and gen ,the master trip is
employed ,which trips the field breaker ,CB and the governor.
| Is This Answer Correct ? | 13 Yes | 5 No |
Due to following points
1)Transient Recovery Voltage (TRV)
2)Higher X/R value
3) Delayed current Zero
circuit breakers was not used after above 60 MW generators.
However please note that now full line of IEEE C37.013
qualified medium-voltage vacuum generator circuit breakers
for voltages up to 24 kV and generators up to 200 MW for
both indoor and outdoor applications are available in
market.
Please note that Circuit breakers applied to generator
switching applications are subject to conditions quite
different than those of a normal distribution circuit
breaker used in industrial, commerical and utility systems.
Distribution circuit breakers, whether of the outdoor
substation type or of the drawout type for use in metal-
clad switchgear, conform to IEEE C37.04 (basis of ratings),
IEEE C37.06 (preferred ratings), IEEE C37.09 (testing) and
IEEE C37.10 (application.)
| Is This Answer Correct ? | 5 Yes | 6 No |
when we r using single phase load and we have power cable of 3.5core with .5 of neutral and neutral is suppose to the returen path of the phase how much current will flow in the neutral.reply.
how to design the heater in temperature control unit to heat 50KL of water?
why we commonly use delta star winding in power and distribution transformers
What is Class and accuracy in CTs? Types of Classes and important of Classes?
How vfd saving power.
can SMPS work in DC supply ?
10 Answers HCL, IBM, Reliance,
define frequency ?
how u calculate ups battery backup
What is the Different between CT Class-0.2 & Class-0.2s ?
How to calculate total harmonic distortion level(THD) in VFD? and how can we reduce harmonics?
how to identyfy cable sizes?
what is the basic difference between fan and home motor if both have single phase induction motor?
4 Answers Engineers India Limited,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)