Answer / sam
Accuracy class of 0.2 means +/- 0.2 % error. But, the
declared accuracy is guaranteed only between 100% & 120%
rating. And, with some increased error, the CT performance
can be guaranteed from 5% loading. Below this load, the
error is not guaranteed. It can be anything.
Normally these classes of accuracy are used for Tariff
Metering by the Utility Company.
In large industrial projects, the project would be
commissioned in steps only. In such a case, initially the
loading will be very low. If the tariff metering CT errors
are haphazard, it may not be acceptable either to the
supplier (in case of negative error) or to the consumer (in
the case of positive error). And the magnitude can be quite
large, say, with a sanctioned demand of 10MVA, even 1%
error means 100kVA.
To cater to such situations, Standards have introduced two
new accuracy classes, 0.2S & 0.5S for tariff metering
purposes. These special CTs guarantee the declared
accuracy, even with 20% loading. And some definite error
can be defined even with a load as low as 1%. Thus they are
suitable for industries where loads are commissioned in
steps or stages.
| Is This Answer Correct ? | 44 Yes | 5 No |
Answer / k.prakashchandra
's' stands for special.0.2s class cts guarantee the the
specified accuracy even at 1% and 120% of rating where 0.2
class cts may not be accurate upto 5% and beyond 100% 0f
rating
| Is This Answer Correct ? | 27 Yes | 4 No |
Answer / rao
For 0.2 Class specified accuracy is 'defined' between 5% to 120% of rated current, whereas for 0.2 S the accuracy is provided between 1% to 120% of rated current. At these secondary current ranges, accuracy is applicable when the burden is between 25% to 100%.
| Is This Answer Correct ? | 1 Yes | 1 No |
what will happen if i connect or change line with phase terminal
What is difference between safe PLC and normal PLC
how we decide scurt (disc) of insulator with respect to kv rating
If the t/f capacity is 500KvA then what is Amps ratting of the main breaker.
all the technical question with answers pleas send your email id ramar_eee@yahoo.com
stand by earth fault protection (51G) for transformer rating 2000 kVA,Dyn11,33/0.400 V. LV NCT ratio and necessary resistor and metrosil values how to calculate
is that any software calculator to calculate the size of cable
what is XLPE cable?
What is the difference between an ELCB and a RCD?
What is meant by line losses, how do you prevent the losses?
Can be ammeter and voltmeter used without CT? if not, what is the reason for that?
3 Answers Elektrotek, Toyo Engineering,
How to obtain B license from TNEB license board. What is eligibility?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)