why we commonly use delta star winding in power and
distribution transformers

Answers were Sorted based on User's Feedback



why we commonly use delta star winding in power and distribution transformers..

Answer / pankaj malhotra

The best way to minimise 3rd harmonics in the transformers
there are two ways. Either transformermer has low flux
density which is not economical and not in use or to make
atleast one winding of the transformer in delta because 3rd
harmonics are absent in delta. Since the requirement of
three phase four wire system in distribution, we commonly
use delta star winding

Is This Answer Correct ?    25 Yes 3 No

why we commonly use delta star winding in power and distribution transformers..

Answer / gunasekaran

one voltage level single earthing is recommended that is at
source for G.T generator is source it is already earthed.if
we use star we have to do the earthing so delta connection
is preferred.for distribution sending end is already earthed
at substation so HV side of the distribution transformer is
delta for LV side transformer is source so star with earthed
neutral. if two earthing is provided zoro sequence current
getting closed path so wave farm become distracted.

Is This Answer Correct ?    6 Yes 5 No

why we commonly use delta star winding in power and distribution transformers..

Answer / arvind sharswat

only most reson because i can gate 3phase and single phase with nutral in delta-star connection

Is This Answer Correct ?    1 Yes 0 No

why we commonly use delta star winding in power and distribution transformers..

Answer / aashish sharma

Delta connection is make at primary side because in delta
low harmonics(3rd,5th and 7th) produce as compare to star
while at secondary side star connection is use to provide 3
phase 4 wire system or we can say that getting singale
phase from 3 phase.

Is This Answer Correct ?    15 Yes 18 No

why we commonly use delta star winding in power and distribution transformers..

Answer / a,karthika

because we can make earthing only in star connection.if
there is an excess amount of power which can be easily
removed by earthing.Hense secondary winding is a srat
winding

Is This Answer Correct ?    1 Yes 4 No

why we commonly use delta star winding in power and distribution transformers..

Answer / vinod meshram

in my thinking we use for getting nutral only because in
delta it is never possible to get neutral.We get neutral on
secondary side for distribution perpose.

Is This Answer Correct ?    2 Yes 8 No

why we commonly use delta star winding in power and distribution transformers..

Answer / e venkat reddy

In Delta connection it requires only three wires to
transfer on power but in star it requires 4 wires to
transfer the same amount on power so we are using delta at
primary side.because availability of neutral we are using
star connection at secondary side. In delta side the zero
sequence is current also zero.

Is This Answer Correct ?    7 Yes 14 No

Post New Answer

More Electrical Engineering Interview Questions

A 3 phase motor operating off 415V system is developing 20Kw at an efficiency of 0.77 and power factor of 0.73. determine:- a)the line current. b)the phase current if winding are delta connected. c)the phase voltage if winding are star connected.

1 Answers  


What are the types of circuit breakers ?

6 Answers   Genco, Super Max,


What is the previous name of Cox's Bazar

1 Answers  


Give the topology of current amplifier with current shunt feedback?

1 Answers  


What happens if we give ac supply to dc shunt and series motors individually

4 Answers   Essar,


back emf of motor at the time of starting ?

2 Answers  


What is the meaning of loop in transformer

1 Answers   AST,


anyone please send transformer parameter design formulas & details of tap changer ? plz i have interview this week its more helpful for me ?

1 Answers  


pls tell us AC plant are how do work and parts name with picture

1 Answers   Mukand,


how can calculated the rating of the 11 KV transformer?

6 Answers   NBCC,


How will be the single line diagram of series trip HT breaker? how it works?

1 Answers   HAL,


What is best method of Calculating Short Circuit current in power system network.

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)