why we commonly use delta star winding in power and
distribution transformers
Answers were Sorted based on User's Feedback
The best way to minimise 3rd harmonics in the transformers
there are two ways. Either transformermer has low flux
density which is not economical and not in use or to make
atleast one winding of the transformer in delta because 3rd
harmonics are absent in delta. Since the requirement of
three phase four wire system in distribution, we commonly
use delta star winding
| Is This Answer Correct ? | 25 Yes | 3 No |
Answer / gunasekaran
one voltage level single earthing is recommended that is at
source for G.T generator is source it is already earthed.if
we use star we have to do the earthing so delta connection
is preferred.for distribution sending end is already earthed
at substation so HV side of the distribution transformer is
delta for LV side transformer is source so star with earthed
neutral. if two earthing is provided zoro sequence current
getting closed path so wave farm become distracted.
| Is This Answer Correct ? | 6 Yes | 5 No |
Answer / arvind sharswat
only most reson because i can gate 3phase and single phase with nutral in delta-star connection
| Is This Answer Correct ? | 1 Yes | 0 No |
Delta connection is make at primary side because in delta
low harmonics(3rd,5th and 7th) produce as compare to star
while at secondary side star connection is use to provide 3
phase 4 wire system or we can say that getting singale
phase from 3 phase.
| Is This Answer Correct ? | 15 Yes | 18 No |
Answer / a,karthika
because we can make earthing only in star connection.if
there is an excess amount of power which can be easily
removed by earthing.Hense secondary winding is a srat
winding
| Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vinod meshram
in my thinking we use for getting nutral only because in
delta it is never possible to get neutral.We get neutral on
secondary side for distribution perpose.
| Is This Answer Correct ? | 2 Yes | 8 No |
Answer / e venkat reddy
In Delta connection it requires only three wires to
transfer on power but in star it requires 4 wires to
transfer the same amount on power so we are using delta at
primary side.because availability of neutral we are using
star connection at secondary side. In delta side the zero
sequence is current also zero.
| Is This Answer Correct ? | 7 Yes | 14 No |
Why the stator is rotated in ceiling fans not Rator?
We have two 1 phase heating coils having same resistance of 25ohm, but during operation one takes 3A and other 6A Is it posiible Pls. explain
why are maintine power factor 0.99 in Eb line? why are used capacitor bank in Eb line? what is the purpose capacitor bank?
4 Answers TNEB Tamil Nadu Electricity Board,
Apparent power is expressed as V * I(Conjugate). Why not in V * I ?
differentional compound gernater used for wielding porpose. why????????//
what is the purpose of slope in the differential relay?why we are using two slope?but in busbar differential we are using only one slope.why?
how to determine motor size for a fan application?
how to check regenerative load in drived motor
0 Answers Hindustan Unilever Limited, NHPC,
how to can we synchronize different capacity of DG sets.60kva& 250kva?
what is a relation of energy in electromagetic field
in power station what is the electrical circuit length of spacing between power transformer and lightning arrestors,for the voltage system of 230kv,110kv,33kv,22kv,11kv?
What is the disadventage of gland earthing(power cable) if any. ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)