Answer / anshul jaiswal
if we use 0-20 mA scale for 0-100%,then 0% will be read in two cases;1)when instrument has any kind of damage problem(not responding case)& 2)for the ground level reading.so we use 4-20mA which shows 4mA for 0%(ground level) & 20mA for 100%(full value) and 0mA shows that instrument has any damage problem.And guyz,in the range of 4-20mA the calibration shows linear characterstic too.
| Is This Answer Correct ? | 30 Yes | 3 No |
Answer / ramali
current output is 4-20 mA.
Let take a transmitter operating range is 0-100%
in this case, 0% is only 4 mA,100%is 20 mA.
Because the transmitter have no power,then its output is
0mA.That means zero , live zero.
zero means there is no process is done.
live zero is transmitter have no power,etc.,
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / p.v.srikumar
because if use 0 -20 mA as 0-100% there is any signal cable
damage or cable open it will show only 0%. if use 4-20mA as
0-100% it will show bad process value(live zero).
| Is This Answer Correct ? | 13 Yes | 9 No |
Answer / yakin patel
Upper all answer is right but its 4ma not 3,2,1 bcz it is calculting prove. Has calcultion
| Is This Answer Correct ? | 0 Yes | 0 No |
without color coding, without nameplate, without multimeter how can you find the type of thermocouple???
why is the sleeve of the cable used for?
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
How would you choose differential range?
What is the different between of rtd and thermocouple ?
Area classification, Equipments, Gas groups, temperature classification, Ingress protection, Fire Extinguishers.
what do you know about Foundation Fieldbus?
what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.
what is difference between HART communication and BRAIN communication?
WHAT DO WE MEANT BY INSTRUMENT MAINTENANCE IN SOFTWARE SIDE.
how do i tune dearator pr control valve using PID. we set the set point is 0.6kg/cm2 now i want 0.5 to 0.7kg/cm2 limits so what should i give p,i,d values. then pls explain how do set pid values for control valve tuning?
0 Answers SEWA, Sharjah Electricity and Water Authority SEWA,
explain how magnetic flowmeter works
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)