In close vessel/ drum why we use d.p. transmitter of -ve
range i.e. (-)500 to 0 mmwc.
Answers were Sorted based on User's Feedback
Answer / venbha123
If the LP leg of the transmitter is kept dry, steam may get condensed in the LP leg because of which the level indication may be wrong. Hence We are using wet leg for LP side of the transmitter, which is initially filled with pure water. When the drum is at zero level, the pressure difference is only the head pressure acting on the LP side - that is 100% level head at LP side. Normally in DP transmitter the HP side pressure will be more than the LP side. In this case since the pressure in the LP side is more than the pressure in HP side the range is mentioned as negative. At 100% level both the head pressures at HP & LP are the same, the DP becomes zero. Therefore the range is mentioned as: from negative value to zero.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / ayaz
IN CLOSE VESSEL/DRUM
we use wet leg mean(low impulse line fill with same liquid)
we know that our measurement is when right then dp is creat
and when we use without low side filling and hp side only pressure the steam create pressure on lp side so dp not create and show wrong indication
so we use fill lp side pressure and address in negative and when hp side posative or actual pressure create a dp in right indication will show
| Is This Answer Correct ? | 0 Yes | 0 No |
why we use only 4-20 ma signal as AI and not 0-20 ma?
2 Answers Honeywell, Oil and Gas Jobs,
WHAT PRINCIPLE OF GAS ANALYSER( CO,CO2,N2)
Can you tell me how we will select RTD and Thermocouples for Temperature applications. I.e How we will choose accurate one for a specefic operation if both having same ranges
Is there any interfacing sofware to build communication between a PC and ER300P model L&T make trivector meter via RS485 port which is available in the meter and is there any data acquisition card available to store the acquired data from the meter into the system
thermocouple output is AC OR DC??
HOW TO CALCULATE WAKE FREQUENCY FOR THERMOWELL???WITH OUT SOFTWARE..
why metallic housing is provided of solenoid valve.
Hi, am aniket, I got engineering degree in instrumentation and control, but as their were no job availabilities for engineer's post I started working as instrumentation technician I kuwait, so my question is is this technician's experience worth for getting the position of engineer?
1 Answers Almeer Technical Services,
wht is snap action switch?where it is used?is there any diff between snap action switch and normal pressure switch?
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
difference between plc and dcs?
I want to apply for the universities in US,but i got the GRE score of (650+300=950)TOEFL 69/120.Is this score sufficient for applying universities please i am married i need to go to US because my husband didn't get H1 yet.please send me suggestion
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)