In close vessel/ drum why we use d.p. transmitter of -ve
range i.e. (-)500 to 0 mmwc.
Answers were Sorted based on User's Feedback
Answer / venbha123
If the LP leg of the transmitter is kept dry, steam may get condensed in the LP leg because of which the level indication may be wrong. Hence We are using wet leg for LP side of the transmitter, which is initially filled with pure water. When the drum is at zero level, the pressure difference is only the head pressure acting on the LP side - that is 100% level head at LP side. Normally in DP transmitter the HP side pressure will be more than the LP side. In this case since the pressure in the LP side is more than the pressure in HP side the range is mentioned as negative. At 100% level both the head pressures at HP & LP are the same, the DP becomes zero. Therefore the range is mentioned as: from negative value to zero.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / ayaz
IN CLOSE VESSEL/DRUM
we use wet leg mean(low impulse line fill with same liquid)
we know that our measurement is when right then dp is creat
and when we use without low side filling and hp side only pressure the steam create pressure on lp side so dp not create and show wrong indication
so we use fill lp side pressure and address in negative and when hp side posative or actual pressure create a dp in right indication will show
| Is This Answer Correct ? | 0 Yes | 0 No |
How much should be the values and/or percentages of these given below factors for a good controller ? Steady state error Delay Rise Time Overshoot Peak Time Settling Time Damping Oscillations & vibrations thanks
how many types of elements are there?
Working principle of vibration sensor?, Type of vibration sensor? , Can we use vertical instead of horizental or vice versa?, if not Reasons?
what is interface level measurement.who can calibrate interface level measurement transmitter online
what is Dry Leg calibration and where is it used
what is the different between deflection type measurement and null type measurement in RTD?
what is the input to be given digital temp controller during the the calibration time?
why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA?
what is Analog input/output & Digital input/output,
2 Answers Bapco Bahrain Petroleum Company,
why use to 250 ohm for hart protocol and why hart communicator not communicate without 250 ohm
Air pressure in a pressure vessel can rise or fall at up to 2.5kpa/s.The pressure is sampled every 0.5 seconds.If range of the the pressure indication is 0 to 1500 kPa, what is the max value of the error due to sampling in % of Span
Lube oil pressure transmitter local it's showing 9.8 kg/cm2 but dcs side it's showing 9.26 like that what is the reason?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)