In close vessel/ drum why we use d.p. transmitter of -ve
range i.e. (-)500 to 0 mmwc.
Answers were Sorted based on User's Feedback
Answer / venbha123
If the LP leg of the transmitter is kept dry, steam may get condensed in the LP leg because of which the level indication may be wrong. Hence We are using wet leg for LP side of the transmitter, which is initially filled with pure water. When the drum is at zero level, the pressure difference is only the head pressure acting on the LP side - that is 100% level head at LP side. Normally in DP transmitter the HP side pressure will be more than the LP side. In this case since the pressure in the LP side is more than the pressure in HP side the range is mentioned as negative. At 100% level both the head pressures at HP & LP are the same, the DP becomes zero. Therefore the range is mentioned as: from negative value to zero.
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / ayaz
IN CLOSE VESSEL/DRUM
we use wet leg mean(low impulse line fill with same liquid)
we know that our measurement is when right then dp is creat
and when we use without low side filling and hp side only pressure the steam create pressure on lp side so dp not create and show wrong indication
so we use fill lp side pressure and address in negative and when hp side posative or actual pressure create a dp in right indication will show
Is This Answer Correct ? | 0 Yes | 0 No |
how ranges is decided for drum level or dearator level,in my pplant i have seen for boiler drum range is -1000 to 1000mmwc, while for dearator -2000 to 0 mmwc ,why they decided to take this range ?
Transducer Input 0 to 230 v ac Output-0 to 10vdc Receiver Input 0 to 10 vdc and Output 4 to 20 ma How?
what is vibration a part of proceess variable? if vibration is a part variables then how we minimize the actual vibration on machine on load,? vision of instrumentation contrl plz ans me IPGDL interview question
Level in tank under vacuum (Ex: Condensate Tank of Power Plant)is measured using D. P. type level transmitter. Tank is subjected to vacuum of 755mmHg. Is it possible to fill wet leg ( i.e. leg connected to top of vessel with low point of D. P. xmtr) with water?. Are there chances of water getting sucked under vacuum? if yes, what is the solution?
On liquid service if PT Head is 18 meters. How much pressure will be exerted on it. If Transmitter is not in service?
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , so what to do for solve this problem. The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
What is solenoid valve? Where it is used?
what is intrument termination what is commisioning
What pressure transmitter.
How to Calibrate Flammable gas detector in field
what is function of sensor, and how is it work , explain with difination
0 Answers Bapco Bahrain Petroleum Company,
how many mmwc are eual to 1kg/sq.cm & can we calculate mmwc into tph?