Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB)
USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO
ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE
THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART
COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?

Answers were Sorted based on User's Feedback



IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO ..

Answer / sam

Ok I think I understand what you are asking. In most SMART
transmitters you have a digital indication on the
transmitter and you want to change what is displayed on this
indicator. You also said that you have changes the unit of
measure inside the transmitter with the HART, and this also
changed the UOM that is displayed.

There is a different parameter that you need to modify to
change the display. The parameter is normally something like
"set disply" or something like that.
Be aware that it will only display UOM or percentage or
display a switching between the two. What ever you have set
your UOM to inside the transmitter, will be displayed on the
indicator as the UOM. You cannot set the UOM to mmH2O inside
the transmitter and then display mBar on the display.
Also note that for a level application this display is
normally set to percentage and not UOM. If the operator look
at it he needs to see % level and not mm level. In a
pressure, flow or temp applications you want this display to
indicate UOM again.
Good luck

Is This Answer Correct ?    6 Yes 2 No

IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO ..

Answer / omer baosman

First of all,parameter's which need to be diagnostic in
transmitter with any of communicator will be in percentage .
Like for flow eg: Kgs,temp eg:cc fh level eg: % ,pressure
psi or bar.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Instrumentation Interview Questions

1.what is controller proportional gain 2.what is the controller intergral action time. 3.A proportional plus derivative controller that has a proportional band of 20% and a derivative action time of 0.1 minutes. Construct the shape of the output waveform for the triangular input if the input rises and falls at the rate of 4 units per minute.

0 Answers  


can we change the range of 3151 model level transmitter of rosemount make? present calibration range is 1000mmwc and want to change it to 2000mmwc

4 Answers  


wht is Zero Elevation and Zero Suppression?

12 Answers  


which type signal in & out in dcs

4 Answers  


HELLO FRENDS ,, I M IN THE MIDST OF TROUBLE .. JUST LITTLE HELP ME... SUPPOSE ,, I HAVE A CLOSE VESSELE TANK ( HEXANE MEDIA ) ,, I M USING ROSEMOUNT 2051 DPT FOR LEVEL APPLICATION .. ITS CALIBRATE RANGE IS.. . 0 TO 950 MMH20 ..I DID CALIBRATED DPT WITHOUT REMOVING IMPULSE LINE OF HIGH AND LOW TAPPING.. & WITHOUT DISTURB 3 WAY MANIFOLD..!!! BUT ,,, DURING CALIBRATION I SELECT RANGE BY HART LRV IS 900 MMH20 & URV IS 1300 MMH20 ,, BUT ,TANK LEVEL SOMETIMES 100 % AT 1100 MMH20 , SOMETIMES 1300 MMH20 ..IN THIS CONDITION .. WHOLE LOOP FAILED ,, MAIN THING IS THAT ,, HOW TO CUSTOME RANGE SELECT ?? AND IF I USED RANGE OVER THE ORIGINAL CALIBRATE RANGE ,,,THEN WHAT ERROR WILL BE COME ??? HOW TO ZERO CALIBRATION OF DPT... HOW TO ZERO TRIM BY MANIFOLD ?? AND FOR TANK LEVEL PURPOSE ... WHICH UNIT I CAN USE ??? IS THERE ANY CALCULATION OR CALIBRATION .. IF YEH .. THEN PLZ JUST GIVE ME CALIBRATION STEPS FOR DPT.. THANKS YOURSSSSSSS

1 Answers   Torrent Pharma,


why the steam drum and deaerator level transmitter range is in negative MMWC to zero

3 Answers   Emerson, Jindal, JKPM,


what is the difference between mmhg & mmwc?. i want to calibrate a transmitter in the range of -100 to 300 mmwc. Which is the reference for calibrate the Tx,if mmwc not available?. Is it mmhg or mmho2?.

3 Answers   UPL,


How to check vortex flow meter is in good condition while we do not having calibration setup?

4 Answers  


Generally in which location ( JB or IO card or DCS) the thermocouple compensation is done.Also where they measure the atmosphere temp ( for compensation) in JB OR DCS panel? How they compensating that atmosphere temp? is any circuit for that ( like in rtd wheatstone bridge)?

3 Answers  


what is the difference between CPC and i/p converter

1 Answers   Siemens,


in the flow caluclation k value how to caluclate.mass flow & volum flow.

1 Answers  


use of split range ? where it is used ? in which control loop it is used ?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)