Answer / raji
IN AN ELECTRICAL CIRCUIT IF THE CURRENT EXCEEDS THE
SPECIFIED LEVEL(FULL LOAD CURRENT) IS CALLED OVER CURRENT.
TO PROTECT THE MOTOR OR ANY ELECTRICAL EQUIPMENT FROM OVER
LOAD(OVER LOAD CAUSES WINDINGS MAY BURN OUT OPEN ETC.,)SOME
CIRCUITS ARE PROVIDED TO PROTECT THE MOTOR THIS IS CALLED
OVER LOAD PROTECTION..eg., IN DOL STARTER OLR IS PROTECT
THE MOTOR FROM THE OVER LOAD
| Is This Answer Correct ? | 10 Yes | 7 No |
Answer / harry
Overcurrent protection is protection against excessive
currents or current beyond the acceptable current rating of
equipment. It generally operates instantly. Short circuit is
a type of overcurrent. Magnetic circuit breakers, fuses and
overcurrent relays are commonly used to provide overcurrent
protection.
Overload protection is a protection against a running
overcurrent that would cause overheating of the protected
equipment. Hence, an overload is also type of overcurrent.
Overload protection typically operates on an inverse time
curve where the tripping time becomes less as the current
increases. Overload relays as well as “slow blow” fuses are
commonly used to provide overload protection.
Some devices provide both overcurrent and overload
protection. A thermal-magnetic circuit breaker has both
thermal (overload) and magnetic (overcurrent) elements. Both
elements operate as described above. Likewise the dual
element fuse has both instantaneous and inverse time
characteristics in the same fuse providing both overcurrent
and overload protection.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / manas
Over current:
The full load current capacity, if it exceeds the rated full
load current it is over current.
Over Load Protection:
Protection given to the electrical equipment to safeguard it
from buring during the fault level or overloading.By
performing tripping action.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / harry
Overcurrent protection is protection against excessive
currents or current beyond the acceptable current rating of
equipment. It generally operates instantly. Short circuit is
a type of overcurrent. Magnetic circuit breakers, fuses and
overcurrent relays are commonly used to provide overcurrent
protection.
Overload protection is a protection against a running
overcurrent that would cause overheating of the protected
equipment. Hence, an overload is also type of overcurrent.
Overload protection typically operates on an inverse time
curve where the tripping time becomes less as the current
increases. Overload relays as well as “slow blow” fuses are
commonly used to provide overload protection.
Some devices provide both overcurrent and overload
protection. A thermal-magnetic circuit breaker has both
thermal (overload) and magnetic (overcurrent) elements. Both
elements operate as described above. Likewise the dual
element fuse has both instantaneous and inverse time
characteristics in the same fuse providing both overcurrent
and overload protection.
| Is This Answer Correct ? | 1 Yes | 4 No |
directional relay is typically used to respond in fault condition who it can be used just as reverse power protection which purely senes direction reversal to operate a circuit breaker?
can anyone show me how the 3 phase power is supplied to socket outlets?
Explain how you intend to work under pressure to meet up with deadline target?
starting torque is increased and current is decreased by using external resistance in a slip ring induction motor. How??
what are the sample questions asking to the test cunducting for electrical superwising lisence test?
cab we add capacitor bank with generator to improve power factor or not??????
in 11kv generators the neutral point is connected to earth via earth coil while in the 33 / 11 kv transformer the neutral point is connected to earth via earth resistor why?
how is working bearing heater?
what is resver in electrical enginnering with answer
How to select earthing strip for 100kw induction motor ?
Can we test the alignment of End shield and stator of turbogenerator without rotor insertion? Also how to fix maintain the alignment at site installation?
What is NUMBER OF RUN for power cable means?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)