Answer / athar abid
As we Know that
KVA = Sqrt 3 . Voltage(V) . Current(I)
Now for 400V (Phase-Phase) syayem
I = 500KVA/(1.732 * 400)
=500*1000/(1.732*400)
=721.7 Amps
There is no standard breaker available with this rating, so
take one step above rating i.e. 800Amps
Hope its clear.
Regards
Athar Abid
| Is This Answer Correct ? | 1 Yes | 1 No |
How is a 100 MVA transformer cooled?
defination of a.c filter
how to identify 3phase....r y b .A new make altnator how to identify R
what are the problems that generally occur in power flows??
Capacitors are used to ... -Reduce the bill of the farmer -Improve the PF
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
WHAT IS METHOD TO DESIGN SIZE OF A 11KV UNDER GROUND CABLE FOR A OUTGOING FEEDER FEEDING 6NOS 250KVA TRANSFORMERS WITH 5KM LENGTH OF FEEDER?
what is the difference between synchronous & asynchronous generators
What is the maximum current carrying capacity for both copper and aluminium cables for 1sqmm?
I have finish diploma electronics and five years experience in electrical field in ht service how can i get c licensce or other electrical certificate
In a three-phase full converter, every SCR conducts for a.60deg. b. 120deg. C.180deg. d.90deg
ON WHAT BASIS LOADS ARE CLASSIFIED AS RESISTIVE,INDUCTIVE AND CAPACITIVE LOADS?.GIVE PRACTICAL EXAMPLES FOR EACH
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)