if in a level tx height is given, how u calculate the ranges
of the tx?
Answers were Sorted based on User's Feedback
Answer / m m chotrani
If you have got the height. Now Pressure = h x d x g
You have h, g is same inside the equipment.
You should get the density of the liquid whose level you
want to measure. suppose you are measuring level from 0 to
100%.your height is say 2000 mm and density is 1.3gm/cc
then P = h x d = 2000 x 1.3 = 2600mm.
Transmitter range will be 2600mm of water column.
Simply multiply height with density to get it in water
column.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / s. kanniyappan
In case of Dry Leg
Span = (X)(Gl)
Hw at minimum level = (Z)(Gs)+(Y)(Gl)
Hw at maximum level = (Z)(Gs)+(X+Y)(Gl)
In case of Wet Leg
Span = (X)(Gl)
Hw at minimum level = (Y)(Gl)-(d)(Gs)
Hw at maximum level = (X+Y)(Gl)-(d)(Gs)
Gl=Specific gravity of tank liquid
Gs=Specific gravity of seal liquid
Hw=Equivalent head of Water
X=Max level
Y=Min level
Z=Distance b/w Datum and Transmitter.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the standard height for stancion supports? and what is the standard mounting height for different transmitters?
What is the working principal of Mass flow transmitter?
what is function of vibration, and how is it work, explain with difination
1 Answers Bapco Bahrain Petroleum Company,
Can a pneumatic control valve work without positioner?
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.
how to calibrate control valves & power cylinders & ultra sonic level transmitters
What is the use of each wire in three wire RTD
I have 475 hart communicator. this is not support any new type of instruments such as tranmitter,fieldvue DVC6200.DVC 200 since i got point out need to upgrade . my questions is how can upgrade new instruments software in my 475 hart communicator. can any answerplease>?
How to calibration a control valve?
warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?
What is Square Root Extractor for?
A flange is used for instrument connection for a system with a design temperature of 316C (600F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)