Profibus DP is a multi-master system. Would it work on RS-485
4W or not, and justify your answer
Answer / carl_ellis
The Profibus DP specification defines the hardware transport
physical layer as 2 wire RS-485. The communications
protocol and the transport layer are both part of the
Profibus DP specification (the separate 2 wire cable for
24Vdc power supply is not involved with the communications).
Any device that passes Profibus DP certification will
conform to the Profibus DP specification.
Therefore, a 4 wire RS-485 device will not work on a
Profibus DP network because it won't be a Profibus DP
device, it does not meet the Profibus DP spec, which is 2
wire RS-485.
Attempting to operate a 4 wire RS-485 device on a Profibus
DP network will only disrupt Profibus DP communications on
the network.
Carl Ellis
Measure First
Is This Answer Correct ? | 2 Yes | 1 No |
Different between control valve and mov
I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration So is there any causes biside this or any permissives ?
what is commissioning & pre commissioning , explain with difination
2 Answers Bapco Bahrain Petroleum Company, Shell,
What is the difference between conductive lined pipe and conductive unlined pipe? Why do we see that?
0 Answers Process Control Technologies,
Name and describe at least 4 status indicators, typically found on a PLC
What standards are used for earthing of field instruments?
Anybody can tell me how to convert mmHg2o /psi to scfm please give me formula of conversion
how to measure temperature from resistance of rtd?and how to measure temp from voltage of thermocouple?is there any formulas?
why do 4 mA serves as 0% not 0 mA?
what are the use of belew gear in general ??
how bolometer is used in temperature measurement ??
What are Sinking and Sourcing IO Cards