how to calculate flow by dp transmitter?
Answers were Sorted based on User's Feedback
Answer / gk3000
You can use Q = sq.root of DP
where Q = Flow rate
DP = differential pressure.
Is This Answer Correct ? | 17 Yes | 6 No |
Answer / jazz
Flow = K x sq. root of dP, where K is the constant of the flow element, dP is the differential pressure produced.This formula assumes that liquid density of media is constant.
Is This Answer Correct ? | 9 Yes | 1 No |
If we interchange HP and LP tapping in drum level measurement and reverse LRV & URV correspondingly.What is the difference between the normal tapping(HP,LP) and reversed tapping(LP,HP)?
wHAT IS BURST MODE IN TRANSMITTER?
canu tell me why 4-20 ma and why not this 3-25ma?please give reason of this value.
Where is wet leg is used?
I have seen the Temperature element (T/C & RTD) installed in process line on 45 degree position, Why? What it mean? How many types of tapping position for temperature elements?
Can anybody explain what is the different between ESD & PLC
can anyone can let me know in Eurotron Micro cal 2+ calibrator in milli amps source mode we are not able to get 20 milli amps output it only produces 1.52 milli amps out, but display shows increase in milli amps , and err6 displays, let me know how to remove the err 6.
how flame detectors sense the flame.
Can anyone explain about ELectropneumatics principle?
1 Answers Forbes Marshall, Step,
units for vibration in power plant
Induction type 1-p wattmeter reads ….. a) true value b) apparent value c)volt ampere value
3 Answers Engineers India Limited,
key phaser where is use and work