how to measure level under ground tank ? which type of
transmitter very accuracy ?
Answers were Sorted based on User's Feedback
Answer / akash
Most reliable LEVEL TRANSMITTERS are GWR or Guided Wave Radar type transmitters. They have no movable parts and are not wetted by the process fluids under normal operation. Hence have a long life.
On the lower end we have position transducers working on the principles of flotation.
Also magnetostrictive type are common in industries and comes at a lower cost.
Is This Answer Correct ? | 0 Yes | 0 No |
principle of rtd
How would i calibrate a new commissioned flow transmitter???
what is diffrence between cascade & three element system.
in control valve is constructed as per API 6D or API 6A, then which standard is used for fire testing of valve?.
Explain the difference between the types of input variables plc?
what are different types of cables used in instrumention how to calibrate a level transmitter online ( rosemount )
how we can check level probe and controller
if we have 380 KVA DG. how to calculate Power Factor. With detailed formula
how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?
loop chech tools list
what is loop folder?
1 Answers Bapco Bahrain Petroleum Company, Hyundai,
We do have a problem in the company that is one PT connected to PlC which is mean 1 out of 1 in PLC system we do have the PAHH is 55 mbar and PALL 8 mbar with a timer of 15 sec for the PAHH the problem started when PAHH goes more than the set point which is 55 it reached up to 71 but due to timer doesn't trip . We force it and we checked everything nothing there . We replaced the transmitter problem still there the reading goes more than the 55 bar the range for transmitte is 0- 60 mbar . So we did loop check , aculaizing valve , wiring all are okay . What the possible causes for this ???
2 Answers National Petrochemical Company,