If I have a motor of 1 MW with 6.6 kV, running at 35% load,
how can I save energy without reducing the load?
Answers were Sorted based on User's Feedback
Answer / mohammad a.monem salama abu se
BY REDUCING THE FREQUENCY
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / k.prakashchandra
You can not lower the load ,capacity, and voltage. To save
energy ,you are left with only reduction of line current to
lessen the I^2R losses.The pf of motor is highest at
full ,or nearly full load.At 35% load ,the pf is less and
hence, the line current is more than required to take the
load (HP)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / maheshbabu calicut
by installing VFD(variable frequency drive)we can vary the speed of induction motors.at 35%load you can run the motor at low speed hence saving power
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Replace the motor with one of lower rating.
| Is This Answer Correct ? | 1 Yes | 1 No |
On monitor it is written that current rating is 2.2 Amps. Is it a monitor current drawing capacity or CPU & monitor. If it is only monitor rating, what will be the rating of only CPU and what will be the power consumption rating of PC, Monitor & Scanner? In net, I learnt that computer consumes only 200-300W while running. With the current rating of 2.2 Amps, how it could be 200-300Watts. Please explain?
How can we define 'Phase'
What is an 86-P or an 86-A trip
how to copy from plc ge fanuc versamax series,all input and output, adress, and printout.
What is the Good Earth resistance value of G.I & Cu. Chemical Earthing & Normal Pipe Earthing?
0 Answers ABC, Reliance Life Sciences, TCS,
Difference between ac parallel circuit and ac series circuit?
what is the abbreviation of MIMIC regarding control and relay panels of power systems????
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
In a parallel circuit dc circuit with two resistors, if you know the voltage, amperage, and one resistors ohms, what formula is used to find the second resistors ohms?
If the earth is a good conductor of electricity, why don't people get shocked every time they walking on earth?
why it is mentioned as 8/10 mva transformer why not directly 8mva or 10mva transformer. please explain me the full detailed reason.
Induction generator has = A negative speed B negative slip C negative voltage D negative current
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)