Depending upon type of cooling employed- with better cooling
10 MVA
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / mohamed ibrahim
I told the same as you said when the full load is loaded
(near to 10mva) the cooling method forced air will be
started. but the interview questioner was refused my
answer. so what will be the answer?.
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / mohamed ibrahim
Ya realy i don't know what he was expected. whatever it is
thanks for your replies guys.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rax
i dont know what tha nterviewer expected from you. but this is
it. the transformer automatically switches form its 8mva capacity to 10mva capacity as the load increases. for this extra load or increased load the natural cooling method can not be used and hence forced air method is used
Is This Answer Correct ? | 1 Yes | 1 No |
what is mean by dual digital protection in the relay field?
what r Grid stations?what r there role.Explain in detail
what is the difference between 50 hz freq. and 60 hz freq.? which is better and economic in them ?
what is the difference between oil surge relay and buchholz relay.
working of diesel generator ?
How to select, design,size & calculate for 11 KV/33KV/66KV/132KV/220 KV/440 KV circuit breaker for HT side of transformer protection/HT distribution protection?
how to calculate the current carring capacity of the conductor
During regenerative breaking= A rotating magnetic field is reversed B slip is positive C torque is positive D slip is negative
Please give the formula for converting from 1 tr refrigeration to kw.
what is meant by residual over voltage & residual earth fault ?
WHY IN AC DRIVES,INPUT PHASE CURRENT SHOW UNBALANCE?
What is DC series motor?