Answer / s. kanniyappan
The measuring the difference between HP and LP of a process
will give dp.
By connecting a pressure source with t-off to master gauge
to the HP side and venting the LP side to the atmosphere,
varying the pressure according to the range and measuring
the mA in series and adjusting zero and span according to
the variation.
In case of of Dry leg connecting a pressure source with
t-off to master gauge to the LP side and venting the HP side
to the atmosphere, varying the pressure according to the
range and measuring the mA in series and adjusting zero and
span according to the variation.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / senthil
CALIBRATION OF A DP TRANSMITTER VARIES DEPENDING ON ITS
RANGE ( POSITIVE OR -IVE TO +VE)
FOR EXAMPLE:IF THE RANGE IS 0 TO 10BAR IS THE RANGE-
U HAVE A FIVE WAY MANIFOLD ON THE
TRANSMITTER.THE POSITION SHOULD BE
- VENT VALVE TO BE CLOSED
-LP ISOLATION VALVE IS OPENED AND VENT TO ATM
- CONNECT THE CALIBRATOR(DRUCK OR HYDRAULIC PUMP) ON THE HP
ISOLATION.
SINCE OUR RANGE IS OF POSITIVE VALUE.WE APPLY CORRESPONDING
PRESSURE ON THE HP SIDE..0,2.5,5.0,7.5,10
FINALLY DONT FORGET TO CONFIGURE IT AS SQUARE ROOT USING
HART COMMUNICATOR IF WE USE IT FOR A FLOW MEASUREMENT..
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / amith.patil17@gmail.com
Differential pressure Can be simply measured by DP
transmitter which is connected to the two tapping point
with difference in pressure in both points this DP is
connected after the Threeway manifold valve whose advantage
to calibrate the transmitter on the site by opening the
middle valve so that to get 4mA,else this Pressure change
in level or the flow causes the material dimension change
which material is connected to transmitter which acts as a
resistance to a wheatstone bridge which generates rhe
corresponding current which is transmitted to the control
room.
| Is This Answer Correct ? | 0 Yes | 4 No |
With N nodes and B branches what will have a network ???
How LVDT position transmitter works on DC supply(24vdc) from DCS, whereas transformer operates on AC supply? pls help..
what should be minimum length and size of impulse line for steam flow orifice and feed water orifice? asked by sanjay parihar
What is the cascade control system and where is use in power plant give the detail with block diagram
State four different types of flow measurement, for gas flow measurement MMSCFD is the common unit expand the unit and specify significance of word S in the unit.
whey we conect ammeter in series and voltmeter in parallel in circuit
what is the difference b/w wet leg & dry leg level method
which type of zones used for boiler? & why ?
How to calculate P,I&D value in PID controller ?
0 Answers Jindal Steel and Power, SAL Steel Power,
how flame detectors sense the flame.
IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
warning lamp does not light, but it does light when the wire from the lamp going to the sending unit is grounded (the part that plugs into the sending unit) what does this indicate)?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)