Consider a level troll.
i am getting a correct value in 4mA and 20mA.
the value in the middle(30 to 60%)is disturbed and i am not
getting the appropriate value.
what is the solution to normalize the level and to get the
correct value..
Answers were Sorted based on User's Feedback
Answer / joe mccabe
a) calc the hyteresis and reset the 4-20 to it, accepting
the deviation in the middle
b) test the amount of deviation @ 4ma,8ma,12ma, 16ma,&20ma
and see if slope is repeatable, write program correction
for slope
c) Your instrument has a hardware issue, do the right thing
and replace it.
Is This Answer Correct ? | 6 Yes | 1 No |
Just Simply Calibrate the transmitter With Different ranges
check for
0% should get 4mA
25% should get 8mA
50% should get 12mA
75% should get 16mA
100% should get 20mA
take reading from Increasing and decreasing Reading. And
According to which plz Set ZERO or SPAN.
Is This Answer Correct ? | 1 Yes | 8 No |
What will the new flow factor if D/P Transmitter is RE-RANGED from 25" WC to 50" WC
what is the procedure to callibrate temp controller ,pressure controller,etc. suppose a temp controller showing error 1.5 degree centigrate how can i minimize it.
0 Answers Sabic, Saudi Aramco Shell Refinery Company SASREF,
what is The specifications for oriface instalation
what is XV and KV valves?
there are two candidates p and q in an election.During the campaign,40% of the voters promised to vote for P ,and rest for Q.however, on the day of election 15% of the voter went back on their promise to vote for P and instead voted for Q. 25% of the voters went back on their promise to vote for Q and instead voted for P.suppose,P lost by two votes,then what was the total no. of voters.
HOW TO CALIBRATE A DRUM LEVEL TRANSMITTER
What is the difference between dry contact and wet contact?
what is basic working principle of Governer in power plant?
How does work A temperature valve or fv control valve in process plz brief me
what is pico fuse? how this different rom othe fuses and how to locate it inside the card?
how checking is done in fiber optic cable? explain the working of RTU?
I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea