what is difference between E/P positioner and I/P positioner.
Why E/P fixed in below actuator and why I/P fixed in other place
Answer / carl_ellis
An E/P transducer is a voltage to position transducer, so
its input signal from the control system is a voltage
signal, like 0-5Vdc. Its output is a proportional pneumatic
signal.
An I/P transducer is a current to position transducer, so
its input signal from the control system is a current
signal, like 4-20mA. Its output is a proportional
pneumatic signal.
E/P and I/P are not positioners and are not called
positioners because each is a transducer that converts an
input signal to a proportional pneumatic signal.
A positioner is a much more than a transducer; a positioner
is a controller.
A positioner senses valve position and regulates its
pneumatic output to control the valve position to the
setpoint defined by the input signal.
Where an E/P or an I/P is mounted is a matter of opinion,
plant standard or convenience, it is not dependent on its
function.
A positioner must receive a valve position feedback signal,
so a positioner must be mounted so mechanical linkage can
sense valve position or when mounted remotely from the valve
(like in high ambient temperature applications) a remote
position sensor is used to feed a signal to the positioner.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
Hi, am aniket, I got engineering degree in instrumentation and control, but as their were no job availabilities for engineer's post I started working as instrumentation technician I kuwait, so my question is is this technician's experience worth for getting the position of engineer?
1 Answers Almeer Technical Services,
what is difference between RTD , thermo couple and thermistor in general ?? (except temperature co-efficient )
what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.
TEMPERATURE VARIATION FOR FREQUENTLY.
can anyone guide me how to get any of the previous year GAIL question papers? are they available? 0n 2nd august i have to take the written test.
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
what is the vital subject for scoring bhel exam&what is the question pattern
To calculate temperature, why we multiply 25 with mV?
A DP Endress and Hauser flow transmitter is always tripping pump at low flow. set point is 74 cubic meter/hr. Thorough impulse line flushing and zero calibration has been done, yet problem persists. What do you think is the problem and how do you rectify this fault?
how to calibrate any tansmiter by loop or hart calibrator
where are following valves are applicable to install. can any valve be installed any line. globe valve butterfly valve boll valve gate valve
how we can check level probe and controller
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)