Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?
Answers were Sorted based on User's Feedback
Answer / madani
Question:Flow in Engineering unit is 40 Tons/hr.
Transmitter calibrated range is 0 to 100 mm/H2o.
For 42 Tons/Hr flow engineering unit,what will
be calibration range of Transmitter.
old flow/new flow = SQ root of old range/SQ root of new range.
Q1= 40 tons/hr, Delta P1 100 mm/h2o
Q2= 42 tons/hr, Delta P2 ?
40/42 =SQ root of 100/SQ root of new range.
Sqaring both sides
Delta P2= 42 sqare X 100/40 sqare.
1764 X 100/1600
Delta P2= 110.25 mm/H2o
For 42 tons/hr engineering unit,the Transmitter to be calibrated for 110.25 mm/h2O.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hiren
tx range:- 0 to100mmh2o= 0 mmh2o= 0 ton/hr,100mmh2o=40ton/hr,42ton/hr=?
100/40*42=105mmh2o. so tx range is 0 to 105 mmh2o
Is This Answer Correct ? | 0 Yes | 0 No |
What should be hight of CONTROL panel for access & OPERATION What is BIS & INDIAN STD for SAME?
Can we measure pressure using differential pressure transmitter? If yes then how?
what is meant by Hydroelectric powerplant?
Coriolis flow meter coil supply is 24vdc but why still we given 230ac for this transmitter let me explained detailed review please
What are the automatic controller MODES?
why we use 24 vdc in instruments mostly?
hello can yoy pls send me previous papers of jindalpower and steel ltd.....'m from instrumentation..... mani1048@gmail.com
relation between flow and differential pressure.
what is the difference between transmitter and converters?
What are different types of orifice plates? State their uses.
NSV type probe stands for
what is the principle of vibration