Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?
Answers were Sorted based on User's Feedback
Answer / madani
Question:Flow in Engineering unit is 40 Tons/hr.
Transmitter calibrated range is 0 to 100 mm/H2o.
For 42 Tons/Hr flow engineering unit,what will
be calibration range of Transmitter.
old flow/new flow = SQ root of old range/SQ root of new range.
Q1= 40 tons/hr, Delta P1 100 mm/h2o
Q2= 42 tons/hr, Delta P2 ?
40/42 =SQ root of 100/SQ root of new range.
Sqaring both sides
Delta P2= 42 sqare X 100/40 sqare.
1764 X 100/1600
Delta P2= 110.25 mm/H2o
For 42 tons/hr engineering unit,the Transmitter to be calibrated for 110.25 mm/h2O.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hiren
tx range:- 0 to100mmh2o= 0 mmh2o= 0 ton/hr,100mmh2o=40ton/hr,42ton/hr=?
100/40*42=105mmh2o. so tx range is 0 to 105 mmh2o
| Is This Answer Correct ? | 0 Yes | 0 No |
Why Bently Nevada use negative voltage for vibration probes?
Ple give me "INDUSTRIAL INSTRUMENTATION AND CONTROL S.k. Singh 3th edition" Solution manual to self-Check Quiz and chapter-wise PowerPoint Slides. Home web-site not available... Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Ple Thanks for all...
What is difference between ESD and PLC please Explain me clearly.
what is disadvantage of field bus (ff)type of instrument
Which type of pressure can be measured by primary elements?
If the average power during generation is zero, why do the analog meters have + and - ?
what is the PID controller?
why I need valve guard and whats different between guard and positioner ??
We Have Two Field bus Pressure Transmitters of Different Sensor Range (I.E One is of Lower range and Another is of Higher Range).Is same Process Line. My Question is Can i provide Saturation Limit to my field Bus Transmitter as We can provide Saturation current limit to HART Instruments. As During Low Pressure Both Working OK ,But During High Pressure, transmitter with Lower sensor range Goes to Fault mode as Beyond its Sensor Limit it can Measure, So may I provide Saturation point Some where to Suppress This Fault during High Pressure.
where can we use viberation transmitter,and how can we control viberation?
If boiler drum level transmitter is not working properly what you will do for resolving the problem in plant running condition?
What is the difference between HMI and SCADA and MMI
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)