Flow tax range 0 to 100 mmh2o ,flow rate 40 tons /hr, I want change flow rate example 42 tons/hr so tx range ?
Answers were Sorted based on User's Feedback
Answer / madani
Question:Flow in Engineering unit is 40 Tons/hr.
Transmitter calibrated range is 0 to 100 mm/H2o.
For 42 Tons/Hr flow engineering unit,what will
be calibration range of Transmitter.
old flow/new flow = SQ root of old range/SQ root of new range.
Q1= 40 tons/hr, Delta P1 100 mm/h2o
Q2= 42 tons/hr, Delta P2 ?
40/42 =SQ root of 100/SQ root of new range.
Sqaring both sides
Delta P2= 42 sqare X 100/40 sqare.
1764 X 100/1600
Delta P2= 110.25 mm/H2o
For 42 tons/hr engineering unit,the Transmitter to be calibrated for 110.25 mm/h2O.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hiren
tx range:- 0 to100mmh2o= 0 mmh2o= 0 ton/hr,100mmh2o=40ton/hr,42ton/hr=?
100/40*42=105mmh2o. so tx range is 0 to 105 mmh2o
| Is This Answer Correct ? | 0 Yes | 0 No |
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
Technician A says that a fuel tank sending unit will have a high resistance only when the tank is full. Technician B says that its resistance when the tank is full depends on whether the sending unit is designed for use with a bimetallic gauge or with a magnetic gauge. Who is correct?
How will you calibrate PID controller? explain with example.
1 Answers Jacobs, Sirte Oil Company,
For a diafhram 1.5 d =kn(p-p0) D4 Where d in deflection in inch k=constant n=no of capdule (P-P0)=Applied pressure in psi D In active dia at capsule. -1.5 d=k to p d being constant -1.5
0 Answers L&T, Shiv Tech Marine Control,
why we are using magnet for calibration of gas detector?
what is the full form of psig.
What is loop1 and loop2 in MTS LT?
What is the difference between working pressure and calibration pressure of a control valve
How does SmartPlant Instrumentation interface with physical design (3D modeling)?
How to convert milliampares into flow??
pls give me presant awerness quistion and answer in my emailid.
How to calibration coriolis flow meter?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)