Dear Friends,
I have a 500KVA transformer supplying whole factory having
3 phase and single phase mixed loads. Power room has
ammeters connected via CTs for individual phase. Now I know
that readings shown on meter for each phase say R,Y and B
are line currents. But when I want to know the total on
transformer do I need to add the currents of all three
phases readings shown on meter or value for anyone phase
will give me the correct power load on transformer for that
point of time.
2. If ammeter shows unbalanced readings for R,Y, B phases
say 150, 250 and 300 respectively so can I assume that 150A
i.e average of 3 will be the 3phase load currents and
remaining will be 1phase currents. Please clarify my doubt.
Answers were Sorted based on User's Feedback
Answer / ahmadmukhtiar
1. The load of R, Y or B will be the total load on
transformer.
2. There must be phase balancing system for protection
otherwise the equipment connected as load will get damaged
if all three phases are unequal.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Calculate load(KVA) on each phase and add
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sakthivel
each phase you find consuming power with use ammeter reading
and volt meter reading
each phase you regulate the load current or equal load
current load you choose
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / abdul karim
If you wants to know the total load of transformer , you must use a watt metrer , OR you will calculate the load in watts of every individual phase then sum of all three phases will be your answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is kvarh? Please define it With calculation General motors ?
wat is the criteria we use the diff. relay ?
How many current ratings of MCB's are in the market? e.g: 1A, 2A, .......upto.
WHAT DO U MEAN BY THERMAL OVER LOAD RELAY& WHERE THEY ARE BUSED
I have a situation to design sub-Distribution board/Panel meant for feeding power sockets. In the incomer CAN i Take TP MCCB with Neutral Link and All the outgoing feeders with to sockets with TP MCCB and Neutral Link? P.S : My System is IT Earthing
How eddy current generation support the idea of train braking?
WHAT IS MEANT BY INSULATION CLEARANCE IN VACCUM?
what is the difference in operation of 3 phase motor when am forward delta connection and reverse delta connection?
on which power factor synchronous motor run
On a 6 KVA UPS we have to provide a DC MCB for Battery bank of 16 nos (12 V 42 AH). What Shall be the current rating of DC MCB ?
0 Answers TNEB Tamil Nadu Electricity Board,
what is the diffrence between single phase and three phase
how the works electronic energy meter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)