Dear Friends,
I have a 500KVA transformer supplying whole factory having
3 phase and single phase mixed loads. Power room has
ammeters connected via CTs for individual phase. Now I know
that readings shown on meter for each phase say R,Y and B
are line currents. But when I want to know the total on
transformer do I need to add the currents of all three
phases readings shown on meter or value for anyone phase
will give me the correct power load on transformer for that
point of time.
2. If ammeter shows unbalanced readings for R,Y, B phases
say 150, 250 and 300 respectively so can I assume that 150A
i.e average of 3 will be the 3phase load currents and
remaining will be 1phase currents. Please clarify my doubt.
Answers were Sorted based on User's Feedback
Answer / ahmadmukhtiar
1. The load of R, Y or B will be the total load on
transformer.
2. There must be phase balancing system for protection
otherwise the equipment connected as load will get damaged
if all three phases are unequal.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
Calculate load(KVA) on each phase and add
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / sakthivel
each phase you find consuming power with use ammeter reading
and volt meter reading
each phase you regulate the load current or equal load
current load you choose
| Is This Answer Correct ? | 2 Yes | 2 No |
Answer / abdul karim
If you wants to know the total load of transformer , you must use a watt metrer , OR you will calculate the load in watts of every individual phase then sum of all three phases will be your answer.
| Is This Answer Correct ? | 0 Yes | 1 No |
Brief use of isolation transformer & how it works.
What is the diffrece between CAPACITOR BANK & CAPACITOR OF MOTOR?
why dc is used in control circuit for mv & hv switchgear instead of ac
Dear Sir I am living in Jaipur Rajasthan now I did complete my b tech degree in electrical engineering in 2012 Sir how I gate certificate of competency for electrical supervisor
What are the factor to be consider for CT selection in 132kV substation?
how we can decide that what value of ht line will come to any commercial building? (ans except According to the building load)
What is the permissible value of earth resistance!
Why don't we provide SURGE ARRESTORS for Transformer feeders?
what is difference between 3.5 core and 4 core cable
Why voltge arev transformed in to 132KV/66/KV/33KV like that
what is the difference between isolation and insolation ? please explain in detail with example.
Could explain briefly of over excitation in transformer.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)