in 132 kv substation ligtning arrestor(120 kv) connected to
line. but line voltage comes to 132 kv, it operate or
not???

Answers were Sorted based on User's Feedback



in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv..

Answer / vettum perumal

Ligtning Arrestors are connected across one phase and
earth. Hence,the insulation of the arrestor shall be
suitable for only phase voltage. that is, 132kv/root3 =
76KV.Hence, these 120 KV LA will operate very well.

Is This Answer Correct ?    26 Yes 0 No

in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv..

Answer / s.rajasekar

the lightinig arrestor connected with line in parrallel
then the volage range will divided by root 3.so the
insulation level of the arrester is suitadable for 132kv
system

Is This Answer Correct ?    15 Yes 3 No

in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv..

Answer / avradeep das

In any conductor of 132 KV transmission line rated voltage
with respect to ground(remember LA is connected between one
conductor/phase and earth)is 76(approx) KV so 120 KV is
adequate

Is This Answer Correct ?    6 Yes 1 No

in 132 kv substation ligtning arrestor(120 kv) connected to line. but line voltage comes to 132 kv..

Answer / jakeer

Yes Deffinatley it will operate.

Is This Answer Correct ?    3 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

Which Motor used in Fan's Motor ?

3 Answers   Matsui Technologies,


what is the maximum load on for 10 kva & 25 kva transformer

8 Answers   ABB, Power Grid,


what is the benift of HT metering & LT metering

1 Answers  


can i use 2000/5A Clamp meter to measure HT cable

0 Answers   century, Engro,


where used impendence relay?

3 Answers  






sometimes, eventhough the HV side of the transformer is opened there is a voltage in LV side .How is it possible?

4 Answers  


WHY WE ARE DOING THE EARTHING IN A SYSTEM. SOME PEOPLE ARE TELLING FOR PROTECTION. WHAT PROTECTION GIVE ME THE CORRECT ANSWER.

2 Answers  


how i prepare for the written test in mahagenco?

2 Answers   MahaDiscom, MahaGenco, Wipro,


what is the equation of insulating resistance of motor???

1 Answers   Birla,


1.what is use of isolation transformer. 2.Differance between KWH,KVAH,KVARH,KVA. 3.Main use of the CT and PT.

1 Answers  


what is difference between sub-station and switch yard.

16 Answers   Bhel, Ravate,


Difference between megger test equipment and contact resistance meter test instruments?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)