Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


Is there any option to replace two Genset of capacity 125KVA
with one higher capacity for same office?

Answers were Sorted based on User's Feedback



Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / kpd

There are not enough details given here to give an
approriate answer.
Office back-up generators are renowned for being crammed in
to the last bit of space the facility has left. Airflows
have to be considered for cooling and also attenuation for
a larger generator is larger again causing prospective
space issues.
Economic constraints may also exist, re cabling a single
feed to the office main board in larger cable to accomodate
the single larger generator may cause issues. Also the
operating logic of any changover contactors or equipment
will massively effect the generator choice.

Is This Answer Correct ?    3 Yes 0 No

Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / k.prakashchandra

That is better

Is This Answer Correct ?    2 Yes 0 No

Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / loboreliance2003

Like Mr.KPD has said that not enough details are given. If
the office already has the setup of 2 gensets of 125kva
with all installed switchgear, panels, changeover switches,
cabling etc. then it is very very difficult and costly to
replace with one single DG set of higher capacity.

If these smaller gensets can be shifted to another location
then okay it can be done. If space is a constrain then well
we can go ahead and do the change. But remember earlier you
had option of running only 1 DG set and saving fuel and
wear and tear.

Once you upgrade to higher capacity then you will have to
run the same even if actual power consumption is much
lower than capacity of DG set.

There are many permutations and combinations involved and I
can help if you can give me all details of the requirement.
williamloboatrediffmaildotcom.

Is This Answer Correct ?    2 Yes 0 No

Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / r.g.walia

yes,there is a clear option. First of all we required a
switch gear of 400A {ACB} And connect the both D G Sets{125}
out put with this switch. After this we connect the new D G
with switch gear.

Is This Answer Correct ?    2 Yes 0 No

Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / william lobo

Looking at your new feedback; it is possible to install a
new DG set of higher capacity. Since the DG sets are on
rental then its more easy. Just ask the DG set supplier (
the one whose performance is satisfactory) to come over and
surely they will be able to give you free advice on how
best the conversion should be done.
The the electrician or engineer who did the job of
providing necessary switchgear and cabling etc for the
additional loads could be contacted and surely he too would
know what best could be done.
But this may entail higher capacity switchgear, cables etc
to be installed in lieu of the existing set up.
Or like the suggestion to provide one 400A TPN and from
here the same original cables could be used to the existing
lower capacity switchgears.
Also one higher capacity new cable is to be installed from
the new DG set to the 400ATPN.

Is This Answer Correct ?    1 Yes 0 No

Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / raghavn

Dear All,

Thanks a lot for your responses.

Let me clear the scenario first.

We have been operating our business in ABC complex first
floor for the past 8 years and due to our expansion we
occupied Sixth floor A wing (two wings are there Viz. A & B
respectively) after occupying A wings again we ramped up our
business further and occupied B wing also after 4 months. in
this case A & B wing has separate DG before our possession
and there were different companies. We are now operating our
business in entire six floor for which we are currently we
are continuing with the existing DG from two different
vendors with different rental amount now i had a thought of
having a single DG instead of two.

hope my answer is clear for your suggestion, let me know for
further details.

Thanks & Regards,
Raghavan.

Is This Answer Correct ?    0 Yes 0 No

Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / raghavan

Dear William,

Thanks for your suggestion. let me start pondering more info
on this. will keep updated on this process status.

Is This Answer Correct ?    0 Yes 0 No

Is there any option to replace two Genset of capacity 125KVA with one higher capacity for same offi..

Answer / raghavan

There is no space constraint here to accommodate and the
ventilation s good in condition.

Thanks & Regards,
Raghavan.

Is This Answer Correct ?    0 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

for 11KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV UG system what will be typical per KM "R" "L" "C" parameter.

0 Answers   wbsedcl,


what are the types of sus station ?

13 Answers   NTPC,


WE are using a 63A MCCB(SIEMENS MAKE) for one of the feeder in LV substation panel.It is supplying to a lighting & power socket DB.Settings in the MCCB is Ir = 63 * 1 , Isd = 8 times of Ir , tsd = 0.5 sec( I2 t off). Sometimes this MCCB is tripping .But no trip in DB MCB. Can anybody tell me reason ? From where i can know about the MCCB settings?

5 Answers  


A 3ph load of 10 KW is equal to how many KW of single phase .

1 Answers  


Greeting to all members, How to calculate spill current when we have different ratio CT and Class for REF(Low Imp) I have 500/1A 5P20 @line side n 400/1A CL.X @ Neutral.

0 Answers   DEWA,


why we use 20 KV, 10KA LA on 22 KV Line

2 Answers  


What are the different types of testing in ht cables?

3 Answers  


How to create a SCADA diagram on PC? I run the DG everyday but i dont know how that animated single line diagram is created.Please answer.

1 Answers  


how the arcing is made in ac electric arc furnace? ( between the three electrodes in any sequences or between the electrode & the charge(steel))

1 Answers  


What will happen if supply frequency change in Transformer KVA rating ?

1 Answers  


What is the importance of earthing?

0 Answers  


CAN WE CALCULATE THE NEGATIVE SEQUENCE AND ZERO SEQUENCE REACTANCE OF A GENERATOR USING ONLY ITS RATED VOLTAGE, KW, PF AND SYNCHRONOUS REACTANCE??? IF YES, THEN HOW??

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)