What is the formula to find maximum load of a DG (Single
phase and Three phase)?
Answer / deepak tyagi
For a DG set full load amps. Formula is
kva×1.39
for example
as we have a DG SET of 1500kva than the full load of DG set will be
1500×1.39=2085 Amps.
Is This Answer Correct ? | 10 Yes | 0 No |
i have 28/32 MVA power transformer with 11/6.6 KC voltage rating and 12%impedance.it have star connection at both side.but it have another thied winding tertiary winding.what is used of this winding. pl tell me
how to calculate the mf of kwh meter,if ct the ratio on meter is 100/5A
How much area is covered by a single lightning arrestor to protect object from lightning strokes ?
What is The function of tvm(tri-vector meter)??
what is the equation of insulating resistance of motor???
explain about RTCC
How to calculate the NGR value for a 2.7MVA Transfomer, 11KV system where the fault current has to be limited to 50A?
Salient pole alternator is more stable, why?
In any Industry, Which voltage level either 3.3kV or 6.6KV to be chosen? Then I would like to know ,Is there any cost consideration or Rating of motor?
which of the following motors is non-self starting?
How to calculate impedance volt in Transformer?
1. what is the power factor of a purely inductive load? (i) Zero (ii) Lagging (iii)Leading (iv) Unity 2. which type of transformer connection is preferred in case of power supply transformer? (i) Star/Star (ii) Delta/Delta (iii) Star/Delta (iv) Zig Zag/Star