Answer / vijay ranipa
if we use 0 to 20ma insted of 4 to 20 ma then we can not
find actual position zero reference output, for example if
we have a motorized valve, it's full close at that time we
get 0ma (0%)reference and at fully open position we get
20ma(100%)reference, in this condition if power supply of is
off then we also get 0ma reference,so here in this kind of
condition we can't get actual result like that gate is
actually close or any other problems as per explanation of
above..
| Is This Answer Correct ? | 32 Yes | 8 No |
Answer / chiru mudra...
There r 2 reasons for this.....
1) All micro controllers, plc, dcs etc., are operated with 1
to 5 volts supply.( Ex: 1v=low, 5v=high).
At the input & output of these devices we use 250 ohm
resistor for converting this 4-20mA to 1-5volts.
ie; 4mA*250 ohms = 1Volt
20mA*250ohms = 5Volts.......
2) If we use this range from 1mA to some range there is a
problem with that.
which is, in industries we use bunch of cables together from
field to control room and vice verse. Due to this there is
some signal distortion in the other cables due to magnetic
induction (electro magnetic induction effect in the other
cables). ie, 1-2 mA current will generate in the unactivated
cables which may cause the mall fn in the total industry.
Ex: 1mA = 0% valve open
2mA = 10% valve open
3mA = 20% valve open.... etc.
| Is This Answer Correct ? | 27 Yes | 5 No |
Answer / vijay
we have field instruments like voltage,current..etc.but
there is an advantage of using 4-20mA,If we are using the
voltage sensors,u know the voltage is resistance
dependence,and resistace of coductor varies as the distance
and temperature,varies.so u may not get the accurate signal
if u prefer for the voltage sensors.using current sensors u
don't find this problems
| Is This Answer Correct ? | 22 Yes | 8 No |
Answer / ajith294
The above answer is correct. we have to need the dead zero,
so we are using 4 to 20 mA instead of 1 to 16 ma
| Is This Answer Correct ? | 12 Yes | 8 No |
Answer / diya.
4-20mA is use in instrumentation feild, bcoz when we consider 1-16mA there is difficult to find error in that...
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / anand
also the signal is linear in 4-20mA range which is not below
4mA or above 20mA.
| Is This Answer Correct ? | 7 Yes | 6 No |
Answer / adarsh choudhary
We used 4 to 20 mA for signal because it is a least affected electrical noise & harmonic signal. Also it is suitable for long transmittance of signal without restricted of resistance of signal wire.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / bhagwan
We use 4-20 mA out put because this signal goes to the field (from control room to the field,) where it is then converted from 3 psi to 15 psi as output to control the flow , tempersture, pressure etc.
In the control room, the same signal is converted from 1-5 volts to read measure flow, temperatures,pressure and at the same time , it is sent back to out put card
to convert 4-20mA. to 3-15 p.s.I. to actuate control Valve.
As the distance beween Control Room & the field is very far, so the loses for transfering 4-20mA. are nill.
| Is This Answer Correct ? | 0 Yes | 3 No |
why we are using drum level control valve air to close?
what is the full form of psig.
what is three element in thermal boiler
Is wet leg type system nessesary to measure water level of steam DRUM? How the transmitter is calibrated to measure this level?
is manifold required for an integral orifice meter?
In field side transmitter voltage droping here no loose connection then what will happen?
please tel me the calibration of pneumatic controler.
What is the formula to convert mv to temperature in k type thermocouple?pls simply elaborate? I got one ans.it is Temp=mv×25°+atmospheric temp,but here what is 25°,i confusef ,so pls????
what is the difference between transmitter and smart transmitter ?
Yokogawa CENTUMVP R6.09 unable to download to Engineering Station with ExaOPC R3.75 The issue is when I try to download the common project section to the Engineering Station (STN) from the HIS in System View, it is unable to connect. The error displayed is: WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. STN0149 ---- ERROR = 2 WARNING = 1 ---- Background: >Updated the ExaOPC software on the STN from 3.60 to 3.75 >STN operating system is Windows Server 2008 R2 >HIS operating system is Windows Server 2016 Stanard Solutions attempted include: >Ensuring all IP addresses are correct and all networked devices can be pinged. >The ability to ping a device using its host name from another device (<ping STN0149> from HIS) >Ensure both devices firewalls are disabled. >The antivirus installed on the STN is disabled. >Ensuring both devices are within the same workgroup. >Added both devices to each other's Host and LMHost files. >Running IT Security tool after changing any administrative settings.
How can we cheak the ENCODER ?
What is micromotion transmitter? What is the porpose of using this transmitter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)