why the secondary winding of the transformer is not open circuited ?
Answers were Sorted based on User's Feedback
Answer / raghavendran.r
I believe that the questioner meant to ask about Current Transformer where it will result in CT BURN OUT if the secondary is left open due to immense flux built up at the secondary.This is why the CT is built to operate in subtractive polarity which will cancel out the flux built from the primary on secondary.
Otherwise in a VT or in normal power transformer the secondary winding should never be shorted bcoz it will result in severe short circuit.which is very dangerous.
Hopes this answers your query.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / priya
I hope the question relates to current transformer.If the secondary is open circuited,the whole of the primary current will work as magnetising current.A dangerously high voltage will be induced in sec wdg bcoz the sec has large no of turns as compared to primary in CT.And this high voltage gives fatal shocks and for this reason secondary of CT must always be earthed.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / arun
In order to carry the load,secondary wdg should be closed
circuited.
| Is This Answer Correct ? | 2 Yes | 6 No |
what is different between earthing and grounding for a electrical eqipment ?
2 Answers BARC, Omega Maritime,
1)what is the function of a frequency inverter? 2)If a few frequency inverter are connected onto a device network,what are the two setting that will ensure the frequency inverter work properly on the network. 3)whats is the name of the input sensor for weigher? 4)How to confirm that the load cellis faulty? 5)Describe briefly the steps to validate that the weigher is working properly? 6)Describe the procedure to validate the flowmeter accuracy? 7)Describe briefly the steps to validate that the tempreture sensor/transformer is working properly. 8)what is the adjustment that need to be done when you are calibrating the temperature transmitter ? 9)what are the safety measures to be taken before disconnecting motor for rewinding. 10)whats is the synchronous speed in rpm of typical 4pole 50hz motor? 11)whats is the formula for kw, ohm's law 12)if a 3phase motor is rated 3kw,415vac,what is it's rated ampere?
1.where in India the maximum transmission voltage is operated? 2.what the methods are used to cool down the transformer?give the specific ratings of the transformer & specific cooling process. 3.how zero & negative sequence reactances are formed in a rotating machine when fault occur in the system?
where can i get the previous years question papers for APGENCO exam.
Can We Apply DC POWER To Transformer???? And Why????
What is AMF Panel????
1.what is the funtion of chiller primary & scondary pumps. 2.what is the use of distribution lines & Types. 3.what is the use the thermal power stations & how much capacity.
What is the de rating factor of cable? What is the importance of the de rating factor in cable select
In how we connect watt meter for open & short circuit test of a single phase transformer.
What Should I Know about Metering, Switchgear and Panels?
when we supply in primary side of transformer then the supply goes in secondary side?how it works?
Discuss about gear cutting machines.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)