if i change range of flow transmitter in th field then does
it need to change range in dcs?
Answers were Sorted based on User's Feedback
Answer / murali -inst.technologist
if range of transmitter changes in field you have to change
the span of the AI in dcs
other wise
transmitter shows correct reading in field side
but dcs get signal in form of 4-20 ma, then flow reading
shows in DCS is as per old DCS span.
| Is This Answer Correct ? | 12 Yes | 1 No |
Answer / www.islamqa.com
we have to configure the range in dcs with the new values.
example:
old range:
o - 625 "wc means 4ma at 0, 20 ma at 625
new range:
0 - 2500 "wc means 4 ma at 0, 20 ma at 2500
Regards,
Ahmed Sabry
Control and Instrumentation Engineer
GPC - General Petroleum Company
ahmedsabry.online@gmail.com
CELL.: 00 2 0121367310
| Is This Answer Correct ? | 8 Yes | 0 No |
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?
what the pid setting in controller
how in the 2 - wire transmitter, 24v supply and the 4ma signal gets in the same path?
Hi, am aniket, I got engineering degree in instrumentation and control, but as their were no job availabilities for engineer's post I started working as instrumentation technician I kuwait, so my question is is this technician's experience worth for getting the position of engineer?
1 Answers Almeer Technical Services,
i feel sq. pipe is better than round pipe pls give comment for this. advance thanks for reply
Why we use 250 ohm resistor in series with HART protocol communication?
13 Answers Chemtrols, Instec, Sabic,
open tank and close tank leavel transmiter about range and calibration
How to control flow variations in magnetic flow maters..... When i will provide proper earthing?
How to find out turn down ratio of Pressure transmitter?
why the discharge pressure of ID fan showing negative at fan running condition.(boiler operating condition.)
What is the working principle of Dozing valve used in cement industry?
If a control valve is hunting means means if we are giving 50% to the cv, the cv will open at 51% then slowly slwoly it will reaches 49% , then it will reaches again 50%, this type of action occured frequntly.. so what to do for solve this problem. The possible cause is in volume booster or positioner's relay.. positioner is double acting .. and make siemens..sipart.The cv is double acting and mounted for anti surge operation, it having 4 nos. volume booster, one sov, one positioner, etc..?
2 Answers Gujarat Fluorochemicals Limited (GFL), Shell,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)