Answer / carl_ellis
The 2 wire transmitter, DC power supply and the load (some
receiver, an analog input on a
PLC/DCS/Controller/recorder/indicator) are wired in series.
The installer 'gets them in the same path', an electrical
series circuit.
The transmitter uses about 3.5-3.6 mA of current as power to
run its own electronics that excite and/or read the sensor,
interpret the sensor's signal and create a scaled output.
A 2 wire transmitter acts like a variable resistor, or
transistor, in that it regulates its internal resistance so
that the output is scaled 4.0-20.0 mA, proportional to the
process variable it is sensing, with the loop current the
ranging 4-20mA.
The power supply voltage must be high enough to drive 20mA
(21.xmA if upscale failsafe is used/selected) through the
load (the input's resistance, wire resistance, any stray
resistance (terminal block). 24Vdc power supplies are the
most widely used power supplies, but most 2 wire
transmitters can operate with power supplies up to about
32-36 volts DC.
Carl Ellis
Measure First
Is This Answer Correct ? | 0 Yes | 2 No |
what is field bus system. need defination
Sir, my yokugava FF TYPE LEVEL transmitter us bad, i don't have spares available, i want to replace it with a Rosemount FF transmitter, please tell me what procedure to be followed and what changes to be done in dcs part.
1 Answers BPCL Bharat Petroleum, OEG,
what is skin thermocouple?
what will happen if transmitter wire get shoted?
how will do square root transmitter calibration
PT RTD Range: -200 to 500 degree celsius If I configured in DCS Lower range and Upper range . In face plate it shows red colour due to overa range how was the characteristics look If the temperature is more than operating range. how was the characteristics look . whether its in Resistance vs Temperature curve is Linear or Non linear
How would i calibrate a new commissioned flow transmitter???
How does SmartPlant Instrumentation interface with physical design (3D modeling)?
how to calculate MMWC values in to Tonns(MMWC values showing in DP transmitter and Tonns value showing in Totalizer). please tell me details?
how to connect transmitter measuring sulfur process? 1-by using long impulse line or 2- by using coated short impulse line
What is calibration?
Regarding MOS (maintenance override switch), I want to know its function and its state ( 1 or 0 when not activated ). An example will be very helpful..thank you.