If a control valve is hunting means means if we are giving
50% to the cv, the cv will open at 51% then slowly slwoly
it will reaches 49% , then it will reaches again 50%, this
type of action occured frequntly.. so what to do for solve
this problem. The possible cause is in volume booster or
positioner's relay.. positioner is double acting .. and
make siemens..sipart.The cv is double acting and mounted
for anti surge operation, it having 4 nos. volume booster,
one sov, one positioner, etc..?
Answers were Sorted based on User's Feedback
Check the following items:
1. Any loose connection or leakage of pneumatic signal.
Check all tube fittings with soap solution.
2.Check the gland packing should not be so tight. If feel
tight, get loose them a bit.
3. Check the pneumatic relays of Postioner. Get clean its
ports, nozzle, flapper etc.
4. Also check, that linkage, feed back mechanical link
should not have any dent, grove, burs etc.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / avinash d. pagar
Also please check volume booster function separately with
out positioner and then set factory setting of positioner.
again calibrate positioner by auto calibration. mostly
hunting and over shooting issues cause by booster error.
| Is This Answer Correct ? | 4 Yes | 0 No |
what is solenoid valve?
what is KV and XV valve
what is the difference between SCADA and DCS?
What is micromotion transmitter? What is the porpose of using this transmitter?
What is inside the PLC panel? How does instruments communicate to DCS computer via PLC? What is the type of wiring in PLC connections? Please answer... Thanks
what is air to open and air to close control valve and difference btwn this...and how to measure milli amp by this...and what is the role of positioner and i/p converter in this..plz help me
What is difference between profibus and modbus communication
what will be the pressure in tank which has the total level of 2 meters and is filled 1.2 meters ?
Can I calibrate the Electromagnetic Flow Meter on line and How.
What are the instrumental diagram of valve.
WHY WE NOT USE 2-20mA,1-20mA,3-20mA or 10-50mA SIGNAL? INSTEAD OF 4-20mA.
6 Answers Hindustan Unilever Limited, Yashmun Engineers,
pls send me the 10 years technical question papers of NTPC AND BHEL
15 Answers Bhel, NTPC, ONGC, UCE,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)