If a control valve is hunting means means if we are giving
50% to the cv, the cv will open at 51% then slowly slwoly
it will reaches 49% , then it will reaches again 50%, this
type of action occured frequntly.. so what to do for solve
this problem. The possible cause is in volume booster or
positioner's relay.. positioner is double acting .. and
make siemens..sipart.The cv is double acting and mounted
for anti surge operation, it having 4 nos. volume booster,
one sov, one positioner, etc..?
Answers were Sorted based on User's Feedback
Check the following items:
1. Any loose connection or leakage of pneumatic signal.
Check all tube fittings with soap solution.
2.Check the gland packing should not be so tight. If feel
tight, get loose them a bit.
3. Check the pneumatic relays of Postioner. Get clean its
ports, nozzle, flapper etc.
4. Also check, that linkage, feed back mechanical link
should not have any dent, grove, burs etc.
aftabmazari@yahoo.com
| Is This Answer Correct ? | 17 Yes | 0 No |
Answer / avinash d. pagar
Also please check volume booster function separately with
out positioner and then set factory setting of positioner.
again calibrate positioner by auto calibration. mostly
hunting and over shooting issues cause by booster error.
| Is This Answer Correct ? | 4 Yes | 0 No |
how can i calibrate E & h make conductivity transmiter . unit : mocro siemens Range :0 to 100 micro siemens sensor : capacitive type
how to caluculate flow by using transmitter?tell me plz I am eagerly waiting for your reply..
2 Answers Agi Glaspac, Reliance Power,
why we use 0.2 to 1.0 kg/cm2 output in control valve
y v r connecting 250 ohms resistor in series when u cummunicate with BT in bench calibration?
hi vishok this is noor plz tell me what type problems will occured i use T/C in the place of RTD in (FEED WATER TANK),plz send ur e-mail address to my ID (mail2noor.hyd@gmail.com)
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
what is different between modbus and serial link? please could anybody give right answer.
why most of the DP transmitters using maximum range as 0-2500mmwc?why not 1000 2000 3000 4000mmwc
WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
how to test rotor &stator earth fault in turbine
If a differential pressure transmitter is calibrated for 0~2500 mmH2o and transmits a 4~20mA dc signal. The transmitter is placed across an orifice plate which is sized to create 2500 mmH2o differential at 5000m3/Hr a) what is the flow rate when the transmitter signal is 13.0mA DC? b) what is the signal output of the transmitter when flow rate is 2500 m3/Hr ?
1)How many tpes of vibration probe and how many tpyes of vibration. 2)how we can calibrate a vibration probe with tk3 3)what is RMS value in vibration measuring application and how we calculate it.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)