Answer / siva
since the losses in the transformer is iron and copper loss
which depend upon the voltage and current but not on the
angle between them
| Is This Answer Correct ? | 25 Yes | 1 No |
Answer / veerendra
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
| Is This Answer Correct ? | 18 Yes | 1 No |
Answer / sangayya s k
the transfor rating is in kva because as the iron losse &
copper losses in transformer depend on the volage & current
so depending on the losses the heat geeration occurs & hence
the rating is explained in KVA to give a detail how much
amount of power it can transfer without getting damaged.
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / okereke okorie daniel
Transformer is rated in kva because the efficiency of a
transformer depends on the copper losses annd the iron
losses which are voltage and current respectively, hence
the rating in kva.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / padmaja
The x'mer rating is in kva because as the iron losses in
x'mer is depends on voltage i.e. as per o.c. test carried
out on x'mer & copper losses is depends on current i.e. as
per s.c. test carried out on transformer.
so depending on the losses reflects voltage & current unit.
hence the rating is explained in KVA to give a detail how
much amount of power it can transfer.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / sangayya sk
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rsundareee
The transfor rating is in kva because as the iron losse
depending on the voltage and copper loss depending on the
current,so total loss depending on the voltage and current
so it,s called kva.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m.gopinath
All ac machines rating is mentioned in kva on name plates
where as dc machines rating is mentioned in kw. In the case
of dc, there is no question of pf as the loads for dc are
always resistive in nature and the pf is always unity. But
in the load can be resistive, inductive or capacitive in
nature in case of ac machines.
Let us calculate current for different loads (ie for
different pfs) in case of ac machines if their rating is
mentioned in kw:
16 MW (not in MVA as in normal case), 132/33 KV T/F
Case 1: For resistive load
HV Current = 16000/(1.732*132*1)= 70 A (approx.)
Case 2 : For inducive/capacitive load at 0.8 pf
HV Current = 16000/(1.732*132*0.8)= 87.5 A (approx.)
observe the above two cases, for a given rating in MW(16 MW)
the current is quiet different and it will depend on the
nature of the load on T/F. This is not in the case of DC as
the nature of load is always resistive.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / uddin
the transformer dus not concider power factor because trans
former's r rating in Kva P= v*i
| Is This Answer Correct ? | 7 Yes | 8 No |
Answer / varun
i m not sure but i thik due to p.f. beacause p.f different
at all time.
| Is This Answer Correct ? | 0 Yes | 5 No |
Please explain me abt PQ diagaram in the power sector.
How to select a D.G set for calculated load of 110kW..?
7 Answers Shakthi Power Systems,
What are the temperature elements?
Explain the operation of damper winding
what is the step by step formula for calculating bus bar phase and neutral size of a panel board.suppose the incomer of panel board is 100A..???step by step answer please
What is value of earth resistance required for substation and equipment earthing and what are the reference guidelines
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
150 hp moter how many kwh in 1 hour and what forfula 3 phase kwh.
5 Answers College School Exams Tests, CPCL, Syncom, Thermax,
What is power factor why we should maintain the power factor unless what will happen
what is meant by bus bar and outgoing/incoming breaker in an electrical/electronic circuit
I have doubt that the supply HZ (very low or high than rated ) may affect the power factor. is it true. ?
Which is is best option for 33 kv line incomer.I am Desinging the panel for new projects and i would like to get Your opinion on this Vcb or sf6. Please help me with your replies. Thanks D p singh
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)