Which is is best option for 33 kv line incomer.I am
Desinging the panel for new projects and i would like to get
Your opinion on this
Vcb or sf6.
Please help me with your replies.
Thanks
D p singh
Answers were Sorted based on User's Feedback
Answer / madhu
SF6 is most reliable, fit and forget. VCB is only available up to 33 kV.
SF6 breakers are maintenance prone and chance of gas leak is more. But SF6 is available from 11 kV to 400 + kV
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / k.prakashchandra
For 33 KV, generally SF6 breakers are used.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / @shim
Use SF6 breaker as it is more reliable & maintenance free.
But be sure that the SF6 breaker is procured from a reputed
manufacturer elso once SF6 gas leakage problem occurs, it
will require to fill gas frequently.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sparta
VCB is better than than the SF6, because , VCB is compact
in size and required less maintance.
| Is This Answer Correct ? | 1 Yes | 3 No |
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test.
WHAT IS THE FUNCTION OF RCCB
please give me all the Alarm .Trip ,Safety Relays & Conditions of Diesel-generators mail me on ashokbabunhce@gmail.com
can we use 7volt DC BATTERY to run a 60watt motor by stepup? Give reason for your answer?
How to calculate Busbar Thickness for Different type of HT/LT panels
what is acceptable leakage current for 33kv cable while doing high voltage test for cable? how to calaulate the leakage current for 33kv or any rated cable?
In which working principal temperature transmitter work.explain in detailed.
Star Delta Diagram with full description
0 Answers SKS Microfinance, Syscom,
On PVC conduit the class "A" "B" or "C" is marked what does it shows. Either its thickness or its composition?
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,
what is function of capacitor in ceiling fan?
how air lock will be removed from generators, how it happens?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)