Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why we are testing cables with DC supply not with AC supply?

Answers were Sorted based on User's Feedback



why we are testing cables with DC supply not with AC supply?..

Answer / deepak tyagi

a.c is non-uniformly distributed on the surface of the
conductor.this means that skin effect comes into play.this
mean that actual resistance increse in case of a.c, while
the d.c is uniformly distributed on surface of the
conductor.

Is This Answer Correct ?    38 Yes 14 No

why we are testing cables with DC supply not with AC supply?..

Answer / mega

Cable Hi-pot test is done with D.C voltage because, if we
do the test in A.C voltage the capacitance effect of the
cable will be charged and will not get the exact value.
That's we are using D.C test instead of A.C

Is This Answer Correct ?    18 Yes 6 No

why we are testing cables with DC supply not with AC supply?..

Answer / udhaya shankar

DC alone is used because we need to measure only the resistance of the winding (or) cable insulation. If we use AC to conduct the insulation test, we will be measuring impedance instead of the resistance as the insulation has a substantial capacitive reactance.

The health of the winding (or) cable is best indicated by its resistance and not its impedance. This is why only DC is used to measure the insulation resistance

Is This Answer Correct ?    6 Yes 0 No

why we are testing cables with DC supply not with AC supply?..

Answer / vineeth kumar c g

in the case of insulation tester (megger) we need to take care of cable insulation resistance not insulation impedance, so we choose DC rather than AC.
In hipot test we give high voltage to the cable and if cable is twisted type then AC will induce an emf due to flux and this will change the value of impedence... (if you only need to measure resistance only)
skin effect may occurs if the frequency is higher than 50 and long length cables.
normally in site DC voltages are used for testing but in manufacturing industry they also use AC tester to calculate impedence also...

Is This Answer Correct ?    2 Yes 0 No

why we are testing cables with DC supply not with AC supply?..

Answer / hashir

Insulation tests, known as megger tests, are carried out using DC because AC introduces reactance, mainly capacitive (AC resistance), into the readings.

The high voltage DC, usually twice the operating voltage, will break down any defective resistance in the insulation.

Is This Answer Correct ?    2 Yes 3 No

why we are testing cables with DC supply not with AC supply?..

Answer / malik

Power cables testing is 2 types IR and Hipot.
1. megger normally D.C, we required the resistance value of
the insulation. AC megger till not to use.
2. Hi pot test, we apply the AC voltage low Frequency(VLF),
we measure the leakage current value. this kit we cannot
measure for the resistance value if the insulation.
so we use AC supply and DC supply for the different
application.

Is This Answer Correct ?    3 Yes 8 No

why we are testing cables with DC supply not with AC supply?..

Answer / guest

because no continuity in a.c. Power supply that y we r tested a cable with d.c. Supply

Is This Answer Correct ?    6 Yes 11 No

why we are testing cables with DC supply not with AC supply?..

Answer / abdul malick

AC supply having frequency

dc supply Fq=0 ...

Is This Answer Correct ?    1 Yes 7 No

why we are testing cables with DC supply not with AC supply?..

Answer / chalapathi

Compartivley DC testing equipment is more cheap than AC, and
it is more easy to produce required test voltage with DC
comparitively AC

Is This Answer Correct ?    9 Yes 18 No

Post New Answer

More Electrical Engineering Interview Questions

what is the formula to find out how many amps generater takes running on full load.

4 Answers  


how to calulate short circuit current for the following: 1.cable connecting 11KV of 22KV/11KV transformer to 11Kv of 11KV/415V transformer 2.what cable size should i use.

0 Answers  


State angle criterion.

0 Answers  


How will you define capacitance?

0 Answers  


to transmit 30kw of power at 30 km what is voltage required

2 Answers   Anglo Eastern, Merchant Navy, NPCIL,


what is tertiary winding in transformer?What is its purpose?

18 Answers   Bhel,


Will MCB tripped off, if there is an electric shock to Human body?

9 Answers  


Why indian power system in 11kv,22kv,33kv,66kv,110kv,220kv ? 2) Why ups required dedicated earth?

8 Answers   Energia, L&T, Sail,


A separately excited dc motor having 2 ohm armature resistsance draws a current of 10A and torque developed is 20 Nm under rated field condtion. the speed of the motor under the rated field condtion , when it is connected to a 100V DC source and delivering 10Nm torque....

2 Answers   DRDO,


will the power consumption remains the same when speed of the fan cnanges??if so y??

2 Answers  


what is the difference between STAR and DELTA connection and application wise how it can be utilizedd ???

1 Answers  


Explain Analog and Digital signals?

1 Answers   UOG,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)