Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why we are testing cables with DC supply not with AC supply?

Answers were Sorted based on User's Feedback



why we are testing cables with DC supply not with AC supply?..

Answer / deepak tyagi

a.c is non-uniformly distributed on the surface of the
conductor.this means that skin effect comes into play.this
mean that actual resistance increse in case of a.c, while
the d.c is uniformly distributed on surface of the
conductor.

Is This Answer Correct ?    38 Yes 14 No

why we are testing cables with DC supply not with AC supply?..

Answer / mega

Cable Hi-pot test is done with D.C voltage because, if we
do the test in A.C voltage the capacitance effect of the
cable will be charged and will not get the exact value.
That's we are using D.C test instead of A.C

Is This Answer Correct ?    18 Yes 6 No

why we are testing cables with DC supply not with AC supply?..

Answer / udhaya shankar

DC alone is used because we need to measure only the resistance of the winding (or) cable insulation. If we use AC to conduct the insulation test, we will be measuring impedance instead of the resistance as the insulation has a substantial capacitive reactance.

The health of the winding (or) cable is best indicated by its resistance and not its impedance. This is why only DC is used to measure the insulation resistance

Is This Answer Correct ?    6 Yes 0 No

why we are testing cables with DC supply not with AC supply?..

Answer / vineeth kumar c g

in the case of insulation tester (megger) we need to take care of cable insulation resistance not insulation impedance, so we choose DC rather than AC.
In hipot test we give high voltage to the cable and if cable is twisted type then AC will induce an emf due to flux and this will change the value of impedence... (if you only need to measure resistance only)
skin effect may occurs if the frequency is higher than 50 and long length cables.
normally in site DC voltages are used for testing but in manufacturing industry they also use AC tester to calculate impedence also...

Is This Answer Correct ?    2 Yes 0 No

why we are testing cables with DC supply not with AC supply?..

Answer / hashir

Insulation tests, known as megger tests, are carried out using DC because AC introduces reactance, mainly capacitive (AC resistance), into the readings.

The high voltage DC, usually twice the operating voltage, will break down any defective resistance in the insulation.

Is This Answer Correct ?    2 Yes 3 No

why we are testing cables with DC supply not with AC supply?..

Answer / malik

Power cables testing is 2 types IR and Hipot.
1. megger normally D.C, we required the resistance value of
the insulation. AC megger till not to use.
2. Hi pot test, we apply the AC voltage low Frequency(VLF),
we measure the leakage current value. this kit we cannot
measure for the resistance value if the insulation.
so we use AC supply and DC supply for the different
application.

Is This Answer Correct ?    3 Yes 8 No

why we are testing cables with DC supply not with AC supply?..

Answer / guest

because no continuity in a.c. Power supply that y we r tested a cable with d.c. Supply

Is This Answer Correct ?    6 Yes 11 No

why we are testing cables with DC supply not with AC supply?..

Answer / abdul malick

AC supply having frequency

dc supply Fq=0 ...

Is This Answer Correct ?    1 Yes 7 No

why we are testing cables with DC supply not with AC supply?..

Answer / chalapathi

Compartivley DC testing equipment is more cheap than AC, and
it is more easy to produce required test voltage with DC
comparitively AC

Is This Answer Correct ?    9 Yes 18 No

Post New Answer

More Electrical Engineering Interview Questions

how can we minimize the off load losses of a distribution transformer which is required to be energized 24x7 ?? capacity of the T/F is 1250 KVA and off load losses are around 2.0 KW.. can we use capacitor bank at the secondary of such a T/F to overcome off load losses? please elaborate briefly...thanks

2 Answers  


What phase difference between p and s winding of transformer

1 Answers   MAHINDRA,


My meter ratio is -/5 and ct ratio is 100/5 now what will be the multiplying factor and how ?

1 Answers  


what is PPI DB?

2 Answers   Priyanka Electricals,


I have 380.KVA Volva Penta DG set. Tell me how to calculate units from KWH reading....

3 Answers  


why electron not flow in open loop,how they know path is open ?

3 Answers  


how to calculate the current carrying capacity of cable

2 Answers   Bhel,


air condition capacity for masjad having 50feet in circal and 35 feet high

3 Answers  


Can we convert off load tap changer transformer to on load tap changer transformer

2 Answers  


what happens if we connect two parallel ideal voltage sources across resistor?what is current flowing through resistor?

2 Answers  


how can we determine size of a cable by knowing the kw or current rating of a load?how can we calculate the resistance box of a slip ring motor?

0 Answers   TK Group,


How will A Medium voltage circuit breaker(11 kV voltage level) operate under short circuit fault condition whether It is having short circuit release like Low voltage circuit breaker or relay should be given?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)