why we are testing cables with DC supply not with AC supply?
Answers were Sorted based on User's Feedback
Answer / deepak tyagi
a.c is non-uniformly distributed on the surface of the
conductor.this means that skin effect comes into play.this
mean that actual resistance increse in case of a.c, while
the d.c is uniformly distributed on surface of the
conductor.
| Is This Answer Correct ? | 38 Yes | 14 No |
Answer / mega
Cable Hi-pot test is done with D.C voltage because, if we
do the test in A.C voltage the capacitance effect of the
cable will be charged and will not get the exact value.
That's we are using D.C test instead of A.C
| Is This Answer Correct ? | 18 Yes | 6 No |
Answer / udhaya shankar
DC alone is used because we need to measure only the resistance of the winding (or) cable insulation. If we use AC to conduct the insulation test, we will be measuring impedance instead of the resistance as the insulation has a substantial capacitive reactance.
The health of the winding (or) cable is best indicated by its resistance and not its impedance. This is why only DC is used to measure the insulation resistance
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / vineeth kumar c g
in the case of insulation tester (megger) we need to take care of cable insulation resistance not insulation impedance, so we choose DC rather than AC.
In hipot test we give high voltage to the cable and if cable is twisted type then AC will induce an emf due to flux and this will change the value of impedence... (if you only need to measure resistance only)
skin effect may occurs if the frequency is higher than 50 and long length cables.
normally in site DC voltages are used for testing but in manufacturing industry they also use AC tester to calculate impedence also...
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / hashir
Insulation tests, known as megger tests, are carried out using DC because AC introduces reactance, mainly capacitive (AC resistance), into the readings.
The high voltage DC, usually twice the operating voltage, will break down any defective resistance in the insulation.
| Is This Answer Correct ? | 2 Yes | 3 No |
Power cables testing is 2 types IR and Hipot.
1. megger normally D.C, we required the resistance value of
the insulation. AC megger till not to use.
2. Hi pot test, we apply the AC voltage low Frequency(VLF),
we measure the leakage current value. this kit we cannot
measure for the resistance value if the insulation.
so we use AC supply and DC supply for the different
application.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / guest
because no continuity in a.c. Power supply that y we r tested a cable with d.c. Supply
| Is This Answer Correct ? | 6 Yes | 11 No |
Answer / abdul malick
AC supply having frequency
dc supply Fq=0 ...
| Is This Answer Correct ? | 1 Yes | 7 No |
Answer / chalapathi
Compartivley DC testing equipment is more cheap than AC, and
it is more easy to produce required test voltage with DC
comparitively AC
| Is This Answer Correct ? | 9 Yes | 18 No |
what is the working of air drayar
What are the types of feedback oscillators?
what is the thumb rule or formula for cable size and current ratings
Diffrectiate between earthing and neutral
how i caculate the cable size for power factor correction unit for example 300kvar
what is the differance between HT motors And LT MOTORS.
0 Answers Empire Vitrum Glass, Sappi,
two transformers of the same type, using the same grade of iron and conducting material, are designed to work at same flux and current densities, but the linear dimension of one are two times of the other in all respects. The ration of kVA of the two transformer closely equal to................? options: 16, 8, 4, 2
is it possible to give the total load from the supply generator's maximum in practical?
being an electrical engineer why you wanna come into software i have an very good academics what answer i have to give
WHY HUMMING SOUND OCCURED IN HT TRANSMMISSION LINES?
Why do we will ground the positive terminal in electrostatic precipitator
why we use star connection in HT motor? and delta connection in LT motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)